ECN Forum
Posted By: Cinner Minimum spacing of grid on... - 06/02/06 02:41 AM
Does anyone know where to find the minimum spacing of grid on netting protecting a luminaire in a gymnasium in the code book?
Posted By: YORKIE Re: Minimum spacing of grid on... - 06/04/06 05:44 PM
You did not say what type of fixture, the only rule that I know of is 26-608 which refers to arcs and globes this says 32mm. Hope this helps.
Posted By: Rick Kelly Re: Minimum spacing of grid on... - 06/05/06 03:40 PM
There is no "minimum" requirement in either the 19th or the 20th edition of the CEC.

Rule 26-608 would apply only if the device in question is an "arc' lamp.

Rule 30-316 states that "lamps shall be guarded". So if the guard is adequate to the task, the CEC requirement is met.
Posted By: mikesh Re: Minimum spacing of grid on... - 06/09/06 08:48 PM
You would need the Standard for wire guards and is not covered in part 1 of the CEC. A manufacturer of wire guards might have a copy of the standard.