Posted By: Oh Well razor outlets - 12/14/05 07:17 PM
Years ago before GFI receptacles there were razor outlets which I believe were simply 1 to 1 isolation transformers. Is this means of protection still acceptable especially in a circuit which tends to nuisance trip a GFI? In fact is anything permissable in lieu of A GFI?
Posted By: dougwells Re: razor outlets - 12/14/05 07:20 PM
Must be GFCI protected what is causing a nuisance trip . BTW Next code cycle calls for GFCI within 1 meter of kitchen sink.
Posted By: Check Pilot Re: razor outlets - 12/14/05 11:02 PM
Anyone know if there are there any GFCI'S available as split receptacles yet? Or will retrofits in kitchens now require installation of ganged GFI's in the panel board? If so, that can get expensive for the owner.
Posted By: Sandro Re: razor outlets - 12/14/05 11:52 PM
Er, in lieu of split receptacles, CEC allows a 12-2 20 amp t-slot type receptacle on either side of the sink with GFI protection. No need to worry about split receptacle gfi's.