Posted By: frank nikita - 03/27/04 12:27 AM
Hospital grade switches have ground screw.I've told been told that since the screws ground the device it's not required?I told them if it's there use it but they want the rule#.
Posted By: crash Re: nikita - 03/27/04 02:50 AM
I think that 24-104(2) might be it. "...permanently connected equipment shall be bonded to ground by copper...conductors..."

[This message has been edited by crash (edited 03-26-2004).]

[This message has been edited by crash (edited 03-26-2004).]
Posted By: Tony Moscioni Re: nikita - 03/27/04 08:26 PM
Frank,

Although, it's a good suggestion, there is no requirement in the Ontario Electrical Safety Code, or the CSA/Z32-99 "Electrical Safety and Essential Electrical Systems in Health Care Facilities", to have the switch bonded to ground.

Tony Moscioni
Electrical Inspector