Posted By: cgw CAT 6 minimum radius - 01/30/14 05:00 PM
For a conduit installed for data cable (e.g. conduit from wall box up to above ceiling) - What should the minimum radius of the elbow be?
Posted By: WESTUPLACE Re: CAT 6 minimum radius - 01/30/14 06:08 PM
4 times the diameter of the cable is the min, for regular bends 50mm is the min.
Posted By: Tesla Re: CAT 6 minimum radius - 01/30/14 11:15 PM
Radius in such situations is almost never an issue.

The crippler is the size of the conduit.

Typical minimum for trivial need: 3/4"

Robust data-com spec out 1 1/4" drops -- for which j-boxes are in mass production (yet special order from your distributor -- such big KOs have to be spec'd) (4-11s)

It's not uncommon for the drops to have no elbow at all. Instead, the drop is a sleeve capped by a plastic bushing -- typically a white nylon style -- Arlington pitches theirs all the time in EC Magazine.

It's common for the spec's to call out for bushed entries, BTW. Bare pipe won't do.

%%%%

Eriksen sells a bender that kicks out mild sweeps in EMT.

It's popular in the data-com world, too.

http://www.ericksenbender.net/

This is usually a company tool. Its sweeps are so gentle that it's possible to go to down a size for data-com sweeps. (ie, 1" replaces 1 1/4") If you do this often enough, then the bender pays for itself.

[ Note: downsizing data-com drops is only possible if you've got the data-com contract. In all other cases, you're in the blind -- and will have to follow the contract spec's. These are usually worked up on the most conservative (oversized) basis so that the writer doesn't get bit by final results.]

%%%

In all cases, never attempt to get away with 1/2" EMT.

%%%

© ECN Electrical Forums