we were called to disconnect an AC roof unit at a condo so roofers could do repairs. My guy went out turned off power disconnected the unit taped the wires the power was turned back on for the heat unit to run. Got a call from the manager to return and reconnect.My guy went out and reconnected the next day. I billed the job . A few days later I recieve a letter with a bill from an AC company from the roofer. It stated in the letter that my guy left a bare wire that contacted the freon line and blew a hole in it requireing repair.I questioned my guy and he assured me all wires were taped and he even taped them together so it would be easier for the roofer to pull the wires thru the new plywood deck they were laying.I called the roofer and he said they were taped just not good enough he also claimed they didn't touch the wires.Now I am stuck with a 500 dollar bill.What burns me is I was never called about this and was blindssided with a bill.I would like to tell the roofer to go pound sand for not getting in touch with me.
When we disconnect equip we Have to make safe. I would have to put those wires into a box and cover.even if it meant a second trip to have the circuit fed though the plywood.
tapeing flying wires is not "make safe" here
I'd have probably put wire nuts on the ends prior to taping. I still don't buy the fact that the end came in direct contact with the refrigerant line so "innocently". Unless it was a really poor taping job, I'd say that someone isn't being honest.
HVAC is operating his margin improvement program. Without human intervention the odds of arcing directly to copper without blowing the C/B must be judged zero.
Go up with a test example of grounded copper pipe...
A jumper ( use personal protective equipment ) will establish that the C/B pops on such a bolted-short.
BTW, I'd never consider e-tape enough to call it safetied off.
Much more likely his troops discovered that they were pulling hot conductors -- the hard way -- and this fee is their retaliation for your man's incompetence.
That the customer would re-close the C/B in cold weather must be considered a given.
A note at the RTU explaining the relevant breaker and your company phone number should have been left behind as standard policy. I would also inform the HVAC tech that the RTU has an electric booster for its heat pump; expect customer will re-energize.
Always assume that the property operator will violate OSHA logic.
Remember the typical HVAC tech is up there freezing his tail off -- rushing the job -- of course.
If he gets zapped and falls off the roof, you should be expecting a lawsuit to spread the pain.
The roofers damaged the line and don't want to pay. Put up a fight. You might have to pay but at least your guys will see that you believe them and stand up for them. For the future, you need a policy that the wires will be disconnected at the feed end. Not doing so is just lazy, anyway. In addition to disconnecting, you also need to make the ends look safe. Tape is enough for a dead wire.
I have to go with the majority on most of this. Disconnecting & taping 'hot' wires and then re-energising the circuit is not acceptable practice. SOP is terminate at the source; ie: remove conductors from lugs of source breaker and make safe there.
Reading your starting thread, I take it that your man re-energized the circuit for 'heat' which I take as an energized feed was still present at the RTU.
Was any evidence of the damage offered to you? Pictures, damaged piping, etc?
Yes, it would have been nice if the roofer/HVAC guys called you, and who did what, and when did the damage occur?
Ever work with these guys before? Financial 'wash' possible? (Your service fees vs. the 'bill')
You may also consider the 'bill' as a wake up call for your man, it could have been a lot worse than a freon line damaged if a person was injured or worse.
We have set a new protocol for the temporary disconnecting of wires and I have given the tech a warning about this serious safty violation and that it will result in termination if it happens again.
At a bare minimum, wire nuts and plenty of tape, with ample instructions. Without more to go on I guess I would have attempted to isolate the RTU wires from the circuit. I presume heating unit and RTU are seperate pieces of equipments? I would also fight the bill on principle. If you call BS on my work, you better back it up.
Sparky in Alaska...
I've never seen separate feeds...
Instead, they are on one feeder...
The 'Booster' is a resistance coil based on pure kilowatts.
It is dropped in -- at the 'last moment' by the HVAC contractor during the job.
And HOW PLEASANT IT IS TO DISCOVER A HUGE BUMP IN THE PEAK LOAD AT THE PANEL AT THE LAST SECOND....
I guess my main complaint is that I was never notified of a problem and was just sent a bill.I dont mind fixing a problem I just want the chance to do it. I also would have liked to have seen the problem so that I could address it with the tech .
Rewire, I got hit with a similar "invisible" bill for a hole that was poked through the roof in a brand-new 10-story office building. They swore that we drilled through the roof decking, through 2" of Styrofoam, 2" of other "whatever", then the rubber membrane, the tar, gobbledy-goop, rocks and what have you.
There were crazy rains and the flood damage was absolutely unbelievable throughout the building.
We proved that we were simply shooting sheet metal screws into the roof decking on the bottoms of the corrugations, which is perfectly acceptable. It turned out that the alarm contractor had been using a 1/2" SDS hammer drill on each floor for their mountings and they forgot that they had reached the top level.
We had to pay a huge amount of money in legal fees to defend ourselves (paid by the insurance company fortunately), but in the end, it was proven that the other contractor was the culprit. They had drilled the hole and just packed it with Duxseal within six inches of one of our attachments.
Stick to your guns and demand details. I'm sure that the cost of this bill is equal or less than your insurance deductible, but sometimes you need to waste the money just to prove a point.
Wires outside of a box with a cover on it are live wires. At the very least the wires should have been removed from the breaker and if that is too much trouble then your service technician should have installed a lock and tag on the breaker. Take a photo of the tag too. that cable should never have been energized and should this have come to the attention of an OSHA inspector I'd guess the bill might have been closer to 5 grand plus the ac repair. Breakers left in the off position are an invitation to turn them on and even a piece of tape across the breaker is not locked off.
Electricians are repudedly the smart guys on a jobsite but how smart is it to leave the safety to a roofer?
Sorry to pile more on. A mistake was made but the next mistake must be avoided.