Posted By: George Little T- tap - 05/20/05 12:39 AM
Can you T-tap in a fire alarm system for addressable devices? Code references please.
Posted By: Yoopersup Re: T- tap - 05/20/05 01:03 PM
All map net systems per UL listing can be T t_-Taped , Even the horns and lights if your using the approved type.
Posted By: Ron Re: T- tap - 05/20/05 05:20 PM
You can t-tap a Class 'B' addressable SLC loop if the project specifications permit. No code violation.
A class 'A' loop cannot be t-taped.
See https://www.electrical-contractor.net/ubb/Forum2/HTML/002083.html