ECN Forum
Posted By: George Little Well casing cap - 02/27/05 03:58 AM
What is the best way to ground/bond the metal cap found on the top of some well casings? Some of the casings (about 50%) are non metallic with a metal cap that could become energized.
Posted By: shortcircuit Re: Well casing cap - 02/27/05 10:20 AM
george...thought we determined that isolated sections of steel need not be bonded [Linked Image]

How about braided bonding jumper to the cap terminating to a lug bolted to a tapped 1/4-20 hole in the cover.

It would be better if they used a non-metalic cover with the non-metalic casing IMO.Haven't seen other than metel casings around these parts.

While were on the subject of wells, do the installations that you see have a disconnect at the casing for servicing the pump?

Most of the installations around here have no disconnect at the casing for the pump motor down in the casing and the wiring extends inside the dwelling to a location where a storage tank is, then through the pressure switch, then to the breaker in the service. The breaker at the service being the only disconnect for the installation.Wouldn't this be a violation of 430.102(B)

shortcircuit
Posted By: George Little Re: Well casing cap - 02/27/05 01:26 PM
430.102(B) Exception (c) uses the word "impracticable" and the definition is impossible, infeasible, unattainable and words like that. So certainly the motor at the bottom of the well fits that exception with respect to locating a disconnect "within sight"
Posted By: George Little Re: Well casing cap - 02/27/05 01:32 PM
More on well casings: There is concerns about the well cap being energized because there is a splice right there and usually the well driller makes that splice and one can only hope he has the right talent and materials to make a good splice. I'm also hearing that there is a lug on the underside of this cap with a green screw that should be utilized,
Posted By: shortcircuit Re: Well casing cap - 02/27/05 04:04 PM
IMO...I don't see how locating a disconnect next to the well casing is "impracticable" and would be as close as you can practically get to being in sight of the pump. It would definitely lessen the hazard to service personal from somebody accidentally turning the power on at the panel.

There should be at least provisions to lock the circuit in the open position. Wait a minute...code already says that.

Well to get back on track of your original concern of the metalic well casing cap, I have seen some caps with the ground lug or screw as you describe.

shortcircuit
Posted By: gfretwell Re: Well casing cap - 02/27/05 11:29 PM
I am not sure how they do wells there but here they have an FS box at the well head with a short piece of liquidtite going to the cap. When they "pull" the well they open the splice in that box and disconnect the liquidtite from the box.
I could have installed a disco in the box but I didn't see the point. There is one "in sight" tho in the pump shack about 10' away.


[Linked Image from members.aol.com]

[This message has been edited by gfretwell (edited 02-27-2005).]
Posted By: harold endean Re: Well casing cap - 03/01/05 02:18 AM
Greg,

They should just use a plastic bonding screw! (LOL) Actually most well casings I see here in NJ have the metal cap with a splice point ( and ground point) right underneath the cap. The well installer "SHOULD" install that ground wire. I will check for it on a Final inspection, but the well installer is usually gine by then. So the GC or EC will have to take care of that problem.
Posted By: gfretwell Re: Well casing cap - 03/01/05 02:42 AM
I never saw an electrical inspector when they punched this well. The well inspector only cared that the well was "producing" and that the old well was capped (poured solid with concrete). If this had been a metal cap there was no reason it couldn't have been bonded to the EGC in the splice box.
© ECN Electrical Forums