Posted By: gserve common GES - 11/01/04 12:00 AM
Can 2 meter pedestals side by side (6' apart)share the same GES?.In other words drive 2 rods and connect 1 end of the#6 GEC to 1 pedestal and the other end of the same GEC to the other pedestal? If not, code reference please. Thanks P.S.This is in a mobile home park and the pedestals are fed by 2 separate laterals from the same hand-hole.
Posted By: SteveMc Re: common GES - 11/01/04 03:03 AM
I've installed saw poles (temporary power) in that fashion and passed inspection.