125% and 60deg. - 10/19/04 01:44 PM
Please correct me if I am wrong.
1. For electric heat, the branch circuit size needs to be based on 125% of the full load amps.
2. Conductors (under 100A) need to be selected at 60degC unless the terminations are rated for 75degC.
1. For electric heat, the branch circuit size needs to be based on 125% of the full load amps.
2. Conductors (under 100A) need to be selected at 60degC unless the terminations are rated for 75degC.