Posted By: nojkj .14 awg wire been for 20 amps branch cir - 10/17/04 04:30 AM
When can I use no 14 awg for 20 amp branch circuit I have been looking into 240 4 D

Thanks nojkj
Under specific conditions you can use 310.16 to size motor conductors.
Posted By: Ryan_J Re: .14 awg wire been for 20 amps branch cir - 10/17/04 05:05 PM
See 240.4(D) and notice the refence to 240.4(E) and 240.4(G).