Posted By: shortcircuit pool bonding - 08/22/04 10:50 AM
Can you guys recommend a method to check an exsisting inground swimming pools bonding connections where they can't be seen...to a metal ladder or a diving board for exsample.Would a simple continuity test between the exposed #8 at the motor and the ladder be sufficient?
Posted By: gfretwell Re: pool bonding - 08/22/04 03:27 PM
You are going to need something very accurate in the sub ohm range to tell you much. I'm not sure what the resistance would be if you just had a ladder cup stuck in wet concrete but I bet it is a fairly low number.
I have an Ecos tester that might work. It can prove less than 1 ohm under a load.