Posted By: shortcircuit cooktops - 08/03/04 01:10 AM
We set up a residential kitchen for an electric cooktop by running a 8-3 romex to the kitchen.The owner got a "Melie" cooktop which is 3 seperate units each rated at 2.8 KW ...mounted side by side only 30inches wide each with its own seperate flex wipp with 12 gauge wire in the flex. Can all 3 be connected to the 8-3 romex that we installed and protect them with a 40 amp breaker???
Posted By: electricman2 Re: cooktops - 08/03/04 05:26 PM
Yes. See 210.19(A)(3)exception 1.
Posted By: shortcircuit Re: cooktops - 08/04/04 12:49 AM
Thanx electricman2!!!

shortcircuit