Posted By: Yoopersup V.F.D. calcs - 07/02/04 12:41 PM
30 Hp with V.F.D.
430.6 & 430.150
30 hp =40amps at 460 volts
40x150%=60amps
wire size=3#6s &1#10
Disconnect Switch=60amp
Should disconnect switch be up sized to 100 amp (fuseable).Seems to be hitting it right on the mark? wondered if maybe to close??

75hp 460v 3 phase (96 amps)
96x150%=144 amps
wire size=3#1s&1#8
Disconnect switch =100amps

Hows it look guys don;t have into off name plates of VFD so using 430.6c
Posted By: Yoopersup Re: V.F.D. calcs - 07/02/04 12:43 PM
Opps Disconnect switch 150 amps not 100 amps
Posted By: iwire Re: V.F.D. calcs - 07/02/04 01:41 PM
Take a look at 430.2.

I do not see an option for using the tables as far as the VFD is concerned.

[This message has been edited by iwire (edited 07-02-2004).]
Posted By: Yoopersup Re: V.F.D. calcs - 07/02/04 01:52 PM
430.6c
If the maximum operating current does not appear on the nameplate ,the ampacity determinated shall be based on 150% of the valves given in tables 430.149 and 430.150.
Posted By: iwire Re: V.F.D. calcs - 07/02/04 01:57 PM
I do not see that 430.6(C) changes the requirments of 430.2