Posted By: JBO1960 conduits in concrete floor slabs - 06/26/04 03:19 PM
What is the minimum concrete coverage for conduits/raceways installed in building floor slabs and where is it referenced in the NEC.
Posted By: iwire Re: conduits in concrete floor slabs - 06/26/04 04:58 PM
0"

Table 300.5
Posted By: trekkie76 Re: conduits in concrete floor slabs - 06/27/04 01:05 AM
2" according to t300-5 note #2
" raceways approved for burial only where concrete encased shallrequire concrete envelope not less than 2" "
Posted By: iwire Re: conduits in concrete floor slabs - 06/27/04 02:12 AM
Trekkie, That note only applies to raceways that are only approved for direct burial with concrete encasement.

That note does not apply to RMC, RNC, IMC etc. Those methods can be direct buried without the need of concrete, those methods only need 0" of cover under a building. [Linked Image]

Bob
Posted By: trekkie76 Re: conduits in concrete floor slabs - 06/27/04 10:25 PM
I always thought the 0" meant that the wiring method could't be used in the particular situation. What is considered " under a building"? we are talking about in a slab not under it. wouldn't that be all other locations?
Posted By: JBO1960 Re: conduits in concrete floor slabs - 06/28/04 07:06 PM
It is my understanding that Article 300.5 "Underground Installations" and Table 300.5 was specifically for conduits installed underground or under slabs. No where does the code state for conduits installed "within" floor/ceiling slabs. If you are refering to table 300.5, "All locations not specified below" then for RGS would need to have 6" cover in a slab.
This cant be right.
Posted By: Nick Re: conduits in concrete floor slabs - 06/29/04 12:15 AM
OK how about 300.6(B). There is no cover requirement but it does specifically allow suitable raceways "in" concrete.
Posted By: earlydean Re: conduits in concrete floor slabs - 06/29/04 09:16 PM
The building code (2003 IBC) has this to say:
"1906.3 Conduits and pipes embedded in concrete.
Conduits, pipes and sleeves of any material not harmful to concrete and within the limitations of ACI 318, Section 6.3, are permitted to be embedded in concrete with approval of the registered design professional."

And, generally the cover requirements are the same as for rebar:

TABLE 1907.7.1
MINIMUM CONCRETE COVER

CONCRETE EXPOSURE MINIMUM COVER
1.Concrete cast against and permanently exposed to earth 3"

2.Concrete exposed to earth or weather
No. 6 through No. 18 bar 2"
No. 5 bar, W31 or D31 wire, and smaller 1½"

3.Concrete not exposed to weather or in contact with ground
Slabs, walls, joists:
No. 14 and No. 18 bars 1½"
No. 11 bar and smaller ¾"
Beams, columns:
Primary reinforcement, ties, stirrups, spirals Shells, folded plate members: 1½"
No. 6 bar and larger ¾"
No. 5 bar, W31 or D31 wire, and smaller ½"

Engineers and concrete contractors look at embedded conduit as a necessary evil. Conduit doesn't provide much in the way of strength and can often weaken the concrete if not installed correctly. Keep your embedded conduit runs at least 2 inches back (or structural engineer's requirements) from the finish to avoid "pop-outs", and allow space between the conduit and the rebar for the aggragate to flow all around both. If installing in floor slabs, install the conduit under the wire mesh.