Posted By: Zapper Physical Damage #40 PVC - 01/27/04 01:42 AM
Running 1" #40pvc 3' above grade leval attach to the front of the house in a horizontal way for about 40'. Not subject to vehicles. Will this violate 347-3c (1999 code for NY)
Posted By: Ryan_J Re: Physical Damage #40 PVC - 01/27/04 03:26 AM
"Subject to physical damage" is a term that only the inspector can answer....
Posted By: electricman2 Re: Physical Damage #40 PVC - 01/27/04 02:30 PM
Another point to consider besides protection is expansion in hot weather. This will be a factor with a 40ft. run. I have seen pvc in horizontal runs with sags between supports even when placed the required distance apart. Use metallic conduit IMO.
Posted By: earlydean Re: Physical Damage #40 PVC - 01/27/04 03:03 PM
PVC is great for your application. Just place the straps every foot or two, and the sag will not be noticable. Runs of more than 6-7 feet may have problems with expansion that would pull the fittings apart. If you come and go at the ends with a 90 degree, expansion will be taken up by the sweep, thereby avoiding an expansion sleeve. Lightly sand, and paint the PVC and it will blend into the siding on the house.