Posted By: gserve AFCI requirement - 12/19/03 01:13 AM
Is AFCI required for a bedroom closet light?
Posted By: Jim M Re: AFCI requirement - 12/19/03 01:38 AM
I don't see any reason why it would not require the AFCI protection. The closet is in the bedroom and all bedroom outlets require the protection.
Posted By: PCBelarge Re: AFCI requirement - 12/23/03 02:39 AM
This question has been posted in other forums, my answer is. A bedroom is a bedroom, a bathroom is a bathroom and a closet is a closet. If the prints label it as a closet, 210.12(B) does not require closets to have AFCI protection.

Pierre
Posted By: Jim M Re: AFCI requirement - 12/23/03 04:13 PM
PC,

I would like to pick your brain for your reason. True a closet is a closet. However, if a arc fault started in the closet light would the sleeping people be immune to the fire just because it is in the closet? IMO peoples lives are too special not to add the protection to the closet.
Posted By: earlydean Re: AFCI requirement - 12/23/03 04:27 PM
The Handbook makes it clear that the closet is not part of the bedroom and does not require AFCI protection. But it also points out that it would be logical to provide AFCI protection to these areas, as a branch circuit is in the area. It is perfectly legal to extend the AFCI protection to closets, hallways and the lights in the bathroom.
Posted By: walrus Re: AFCI requirement - 12/27/03 09:51 PM
Glad I saw this as I was going to ask similar questions. Building an addition on side of my home. Its going to be a Master Bedroom and Bath and storage area. It goes up against a kitchen so my new Bedroom shares a wall with my kitchen. I can have all the wiring in a bedroom wall that runs a kitchen without being on an AFCI but if its receptacle in the bedroom it has to AFCI. Not sure I understand why I'm safer after doing that??.
Posted By: Ryan_J Re: AFCI requirement - 12/27/03 09:58 PM
Maybe the same reason you are required to have a smoke detector in the bedroom and not in the kitchen [Linked Image]
Posted By: iwire Re: AFCI requirement - 12/27/03 10:00 PM
By Jim M
Quote
True a closet is a closet. However, if a arc fault started in the closet light would the sleeping people be immune to the fire just because it is in the closet? IMO peoples lives are too special not to add the protection to the closet.

Jim putting the closet on an AFCI might help and you are free to do so.

But is it required?

No it is not required which is what the question was.

I would be willing to bet PCBelarge goes beyond code minimums many times, but his answer in my opinion is right on the money.