Posted By: buckyswider 100A sub redux - 11/24/03 09:50 PM
Wow, spent the afternoon searching the archives re 100A subpanel. Bazillions of posts, opinions, and interpretations, but no consensus, but the safe way(s) to go are either:

1) Install 90A cb on feeder panel for #4 CU;
or
2) Use #3 CU.

(BTW, I plan on THHN).

Question about option #2- the neutral & grounding bars on the main panel are only rated for up to a #4 CU. What do I do with my grounded & grounding wires if I use #3?

Yes, I've removed the bonding jumper from my sub. Will make sure that neutral bars get only grounded conductors, and grounding bars get only grounding counductors.

Thanks!
Posted By: Tom Re: 100A sub redux - 11/24/03 10:41 PM
Check the manufacturers catalog. Sometimes they make an auxilliary lug that will fasten into a couple of the neutral bus holes. I know that GE and Square D make these for their panels.

Tom