Posted By: Branch Bonding - 11/14/03 05:01 AM
I have an outside 200 amp diconnect with a 4 - wire system for a single dwelling, i installed 2-ground rods for my main grounding. The water line service is plastic. Can i bond water lines at sub-panel or does the bond go out to means of disconnect or ground rods.
Posted By: Ryan_J Re: Bonding - 11/14/03 02:15 PM
250.104(A) states that the bonding must go to the service equipment, the grounded conductor at the service, or or a grounding electrode or grounding electrode conductor.
Posted By: Branch Re: Bonding - 11/14/03 02:40 PM
Thanks, thats the way i'm reading it in art:250.104-1. But since this water line is not a ground could this be under (other metal piping) Art:250.104-(4)(b)where the equipment grounding condutor for the circuit that may energize the piping shall be permitted to serve as the bonding means.
Posted By: Ryan_J Re: Bonding - 11/14/03 02:51 PM
I would view "other metal piping" as gas piping, condensate lines, copper air lines, etc...
Posted By: Branch Re: Bonding - 11/14/03 03:15 PM
Thanks Again for your input.
Posted By: Ryan_J Re: Bonding - 11/14/03 06:07 PM
You are welcome