It seems to me that this has been discussed before but I can't locate the thread nor the reference in the 2002 NEC.I think I remembered that it is limited to one conductor.
Chris
I meant to ask about the grounding conductor,
not the grounded conductor
Chris
Posted By: Ryan_J Re: number of conductors under a bus screw? - 09/30/03 01:31 PM
408.21

EDIT: OOPS! Sorry I misread your post. I believe 110.3(B) would apply. Also take a look at article 11014(A), last sentance. "Terminals for more than one conductor...shall be so identified". I believe as long as your terminals are listed for it, you may land more than one EGC on the terminal.

[This message has been edited by Ryan_J (edited 09-30-2003).]