Posted By: Redsy Non-metallics in air spaces - 09/29/03 03:43 PM
Where can I find rules on the use of non-metallic cables & raceways above drop ceilings that are used for air returns?
I thought there were prohibitions, but I can't find anything in the articles on-
LFNC, LFMC, or RNC.

Thanks!
Posted By: Ryan_J Re: Non-metallics in air spaces - 09/29/03 03:57 PM
I don't a have book in front of me, but I think it is in article 300.22 and also in the IMC in section 605.

I'm sorry if I'm wrong on that. It might be 300.12.

[This message has been edited by Ryan_J (edited 09-29-2003).]
Posted By: resqcapt19 Re: Non-metallics in air spaces - 09/29/03 05:27 PM
Redsy,
See 300.22(C). In general you cannot use nonmetallic raceways, however if this is a Chapter 8 application there are some nonmetallic raceways that are permitted. See 800.51(J) for an example. One brand of this stuff looks just like electrical nonmetallic tubing except that it is orange.
Don
Posted By: Redsy Re: Non-metallics in air spaces - 09/29/03 06:06 PM
Ryan, Don,

Thanks for the help!