Wiring an outdoor spa with an enclosed Gazaebo around it and unclear at the distances for the GFI protected light (using GFI breaker) over head and recept on the wall. Checking the code, looks to be 5 feet form waters edge on the recept and 7"6" for the light unless a weatherproof light is used.
Any clearer answers to this?
Thx,
Al D
AHJ in one of the counties I work in says a Gazebo is still an Outdoor installation
This one is completely enclosed from the weather and has a sliding door.
Al,
This may be a good question for your local AHJ.
My understanding is:
If it's considered inside and the fixtures will be less than 7'6" above Tub they have to be GFCI protected and Non-Metallic (or Metallic isolated from contact) per 680.43(B)(1)(c)(2)
Note that the 7'6" is the height above Maximum Water Level, not from the floor.
Bill
So, 5 ft from the waters edge above should be ok as long as it is GFI protected and non-metallic, assuming the gazebo is weather tite. Liquid-tite and plastic boxes should work, correct?
We don't get much rain here in AZ anyway.
It says the fixture must be non-metallic, does that mean I can't run BX cable or flexible conduit to it?
I would submit that an enclosed hot tub is a wet location, just as if it were outside, in the open. I say this because a hot tub is, well, hot, and the hot water will condense on everything- including the inside of your fixtures.