Posted By: dana1028 Bonding Around Reducing Washers - 05/07/03 05:20 PM
Don - I thought I'd throw this at you since you are a wealth of information about the minute details of the code.

In the Mike Holt forum it was stated: "Also bonding is required around reducing washers if the metal raceway is used as an EGC per 250.118".......which led to "Reducing washers to not allow the low impedance path as required in 250.4(A)(3)."

My question: Where is the documentation, code recital, UL or other Standard that supports such a claim?

I have read in Mike Holt's 'Ground & Bonding' and in Soares ' Book on Grounding' that "reducing washers are not suitable for bonding and should always be bonded around"

HOWEVER - neither of these books cite or footnote a study, report, document, or standard that reducing washers do not meet a 'low impedance' criteria.

The reason I bring this up is that both of these books usually refer to studies, standards or the code, etc. in supporting such a statement......AND - how would an inspector be able to support such a requirement to the electrician in the field with 'Soares says so in his book'.?

I know some devices/materials are not tested by UL and as such automatically do not satisfy a standard - but I don't know where to look further to satisfy this curiosity I have around this reducing washer issue.

Thank you for any information you may be able to provide on this subject.
Posted By: txsparky Re: Bonding Around Reducing Washers - 05/07/03 06:04 PM
Are reducing washers listed for grounding ?
Posted By: dana1028 Re: Bonding Around Reducing Washers - 05/07/03 06:29 PM
that's the question! I've looked around the UL! Haven't found anything (not like the UL is real easy to find your way around)... looked on the box from the manufacturer, nothing.

Soares shows various tests using different conduit fittings when clearing faults but don't show any tests for reducers.

ultimately I figure this is a 'listing' issue but haven't found anything in UL.
Posted By: George Corron Re: Bonding Around Reducing Washers - 05/07/03 11:48 PM
Dana1028,
Exactly the point, UL does not list them for grounding purposes, never did, at least for a long time. Article 250 supports bonding around all weak points, and that is why they also must be bonded around, which is the 2nd point.

Soares quotes an IEEE testing procedure, and that is acceptable not only for enforcement with USBC standards, but NFPA documents as well. It was not enforced around here for a long time, but did finally catch up with us.
Posted By: Bjarney Re: Bonding Around Reducing Washers - 05/08/03 12:20 AM
Stamped sheet-metal reducing washers would probably be OK for PVC male adapters with locknuts.
Posted By: harold endean Re: Bonding Around Reducing Washers - 05/08/03 12:21 AM
It would fall under sec. 110-3(b) of the NEC (1999)
Posted By: resqcapt19 Re: Bonding Around Reducing Washers - 05/08/03 07:35 PM
Dana,
I'm not aware of any specific document that says reducing washers are not suitable for grounding, but I'm also not aware of any document that says they are suitable. I'd require bonding based on 250.4(A)(5) and if the contractor doesn't agree, then he can provide me with a document from a NRTL that says they have been tested and found suitable for grounding.
don
Posted By: Redsy Re: Bonding Around Reducing Washers - 05/09/03 11:16 AM
Reminded once again that the NEC provides MINIMUM acceptable requirements. Why the hesitancy to install a bushing that will ENSURE electrical continuity, due to it's listing. (See 250.96 (A))
The potential arcing due to a loosely connected grounding path creates a fire and/or electrocution hazard in the event of a fault.
Do it to it. [Linked Image]

[This message has been edited by Redsy (edited 05-09-2003).]
Posted By: Creighton Re: Bonding Around Reducing Washers - 05/09/03 02:32 PM
All reducing washers are subjected to a Resistance Test and a Current Test by UL. These tests are in the test standard UL 514B, and also in UL 467. All reducing washers currently Listed by UL have been subjected to these tests. Creighton.
Posted By: resqcapt19 Re: Bonding Around Reducing Washers - 05/09/03 05:15 PM
Thanks Creighton. How do they insure contact with the enclosure? Is the installer required, by 250.95(A), to remove the enclosure paint before installing the reducing washers? I really can't imagine reducing washers providing the required low impedance fault clearing path, but if the NRTL says they do, I guess we'll have to accept them. If they are not listed to provide contact through the paint, I would require that the paint be removed. I would expect it would be cheaper to install a grounding bushing, than to remove the paint.
Don
Posted By: Bjarney Re: Bonding Around Reducing Washers - 05/09/03 08:13 PM
As a substitute for reducing washers, one replacement is a threaded reducing bushing with a pair of locknuts. The intent is to yield better ground continuity and increased physical-damage withstand. (Say, limit the size to 2 inch.)
http://www.appletonelec.com/pdf/I-36.pdf is an example of the subject reducing bushing.

Would AHJs in your area accept or reject such an installation?
Posted By: Creighton Re: Bonding Around Reducing Washers - 05/09/03 11:25 PM
resqcapt 19: Do you remove paint around a knockout when installing an EMT connector and a locknut? If you examine the oversize KO you will find raw metal all around the opening. I believe the reducing washers are formed so as to make good contact with this raw metal edge - no need to remove paint. Naturally one must tighten the locknut thoroughly. Bjarney: Sure, I would accept the reducing bushing and I wouldn't remove any paint, depending on the locknut to dig through the paint. Creighton
Posted By: resqcapt19 Re: Bonding Around Reducing Washers - 05/10/03 02:35 AM
Creighton,
In my opinion the teeth on the locknut are designed to meet the rule in 250.96(A). I believe that this is even part of the listing and when this rule was first placed in the code one of the EMT connector manufacturer's made a point, in their ads, that their locknut was listed for grounding without removing the paint. I see no way that a reducing bushing will provide an adequate fault clearing path if the surface paint is not removed.
Quote
250.96(A) ... Any nonconductive paint, enamel, or similar coating shall be removed at threads, contact points, and contact surfaces or be connected by means of fittings designed so as to make such removal unnecessary.
Don

[This message has been edited by resqcapt19 (edited 05-09-2003).]
Posted By: dana1028 Re: Bonding Around Reducing Washers - 05/16/03 09:16 PM
Thank you all for your replies, I appreciate the feedback.