would a fire switch (disconnect before meter)
be wired as the main disconnect for the service? thanks GEO
Posted By:
resqcapt19
Re: main disconnect
-
04/24/03
06:13 PM
Geo,
The only problem is that 230.91 requires that the service OCPD be a part of or be located immediately adjacent to the disconnect.
Don
©