Posted By: aldav53 bath fixtures - 04/10/03 05:04 AM
A light fixture is supposed to be 8' high and 3' out from the top of the bath tub. I assume this applies to ceiling fans too, correct?
Posted By: Redsy Re: bath fixtures - 04/10/03 11:24 AM
Correct. 410.4(D)
Posted By: russ m Re: bath fixtures - 04/11/03 01:41 AM
Just to be politically correct, these fixtures would have to fit the descriptions given.(cord connected, hanging, lighting track, pendants, or as you mentioned ceiling suspended fans.

Russ
Posted By: ccdave Re: bath fixtures - 04/14/03 02:13 PM
Paddle Fans
Posted By: Trainwire Re: bath fixtures - 04/14/03 06:31 PM
What do you do if 3' out from the tub puts you up against the opposite wall of the bathroom?

TW
Posted By: iwire Re: bath fixtures - 04/15/03 12:34 AM
Trainwire, you would have to use a recessed fixture listed for the application.
Posted By: Trainwire Re: bath fixtures - 04/15/03 01:10 AM
Ah, I think I understand,

The fan/light/heater/nightlight that's stuck up into the cieling is ok.

TW
Posted By: Bill Addiss Re: bath fixtures - 04/15/03 02:08 AM
Is a standard ceiling-mounted fixture considered a "Hanging Fixture" as prohibited in 410.4(D) ?

Inspectors?

Bill
Posted By: caselec Re: bath fixtures - 04/15/03 02:30 AM
I don't think 410.4(D) applies to surface mounted wall or ceiling fixtures. If it does apply to surface mounted fixtures it would also apply to recessed fixtures since there aren't any exceptions. The Handbook states that recessed and surface mounted fixtures are acceptable within this zone.

Curt
Posted By: Bill Addiss Re: bath fixtures - 04/15/03 02:40 AM
Curt,

I agree that surface-mounted fixtures are permitted, and have never personally heard any AHJ objections to them, but I think we've got some differing opinions on that here.