Posted By: Joe Tedesco Spacing between conduits, etc... - 02/04/03 05:35 AM
With this rule in mind:

Quote
310.15 (2) Adjustment Factors.

(b) More Than One Conduit, Tube, or Raceway

Spacing between conduits, tubing, or raceways shall be maintained.

How do you determine the proper spacing?

When laying out the conduit, or tubing entries into a gutter, or trough what's the easiest and best way to make sure the holes are spaced apart properly to allow locknuts and or bonding bushings to be used?
Posted By: iwire Re: Spacing between conduits, etc... - 02/04/03 10:13 AM
If I am pressed for space I simply use the biggest component (pressure connector, hub or bonding bushing.) and lay them out right where they are going and push them around till it looks good.

You end up with 3/4" to 1" between pipes, unless using hubs, this close together supports get tough.

Straps are out, Minnis are tough and strut clips must go in before pipe, no room to twist clips.

Am I violating 310.15 (2)?
Posted By: Elzappr Re: Spacing between conduits, etc... - 02/04/03 05:42 PM
Ditto for me,iwire.
I try to space the conduits for whatever is required for inserting the straps after the fact.
What is the purpose for the code reference, Joe? Was that rule made so that things would be neat and tidy, and assure that conduits are actually SPACED for proper ventilation? Or was it done in order to make sure that all conduit entries are facing boxes perpendicularly? How is this rule enforced in practice? Do you see inspectors reserving it for obvious screwed-up cases? Or do you find that inspectors call it every time they see un-even racks? I certainly haven't run into ANY inspectors mentioning it in any re-model or retro-fit jobs I've been on - the places where you frequently find such violations committed by maintenance people(presumably)jamming another 1/2 or 3/4 in an existing rack.



[This message has been edited by Elzappr (edited 02-04-2003).]
Posted By: Redsy Re: Spacing between conduits, etc... - 02/04/03 07:08 PM
NECA's National Electrical Installation Standards #1-2000 (titled "Good Workmanship in Electrical Contracting")has a table that shows spacing for various size conduits. I can't print the table, but it states that these dimensions will allow 1/4" between locknuts.
Posted By: Elec_VA Re: Spacing between conduits, etc... - 02/04/03 11:00 PM
I agree with iwire. I take all the penetrations that I know of and just lay it out depending on the size of the conduit and where it is coming from and the largest part of the connector. Then I try to leave as much room as possible for new pipe. You always need to run it, it seems [Linked Image]
Posted By: Joe Tedesco Re: Spacing between conduits, etc... - 02/05/03 02:12 PM
Redsy was kind enough to take time out of his busy schedule to send this in for us to review:

[Linked Image]

Note: I used the 310 reference only as a way to get to a rule that was related.



[This message has been edited by Joe Tedesco (edited 02-05-2003).]
Posted By: emike Re: Spacing between conduits, etc... - 02/19/03 02:47 PM
I use to use the lock-nuts and space them out on top of the panel. I saw the Marksman tool in one of the magazines and bought one. It gives perfect spacing any size to any size with 7/8" spacing for tight work or 1 1/8" spacing for places where a lot of retrofit work is done. It also spaces the center of conduit from the wall allowing for 7/8" or 1 5/8" strut. THIS TOOL IS AWESOME!
Posted By: nesparky Re: Spacing between conduits, etc... - 02/20/03 06:07 AM
try www.innovativetoolco.com