Posted By: Roger Inspectors strange interpretation - 01/10/03 01:07 AM
I posted this at the M.H. forum also.

Talking to another electrician today who works in another area.

He tells me there is an inspector in this area, who says, when using NM in a commercial building, the NM in attics and basements must be enclosed on both sides, within 15 minute finish rating in living area and attic or basement area.

He said the inspector is using (twisting in my oppinion) the wording of 334.10(3).

I proceeded to tell him I was glad we do zilch in NM work and don't work in this area.

After thinking about it,I thought I would see what oppinions would come up here.

Roger
Posted By: spyder Re: Inspectors strange interpretation - 01/10/03 02:51 AM
I have never run into this before, but he may have a point after reading 334.10(3). Learn something new everyday. I almost always use MC cable anyway for commercial.
Posted By: sparky Re: Inspectors strange interpretation - 01/13/03 09:31 PM
requiring all residential basements to have a 15 min. fire rating would be a stretch...but what trade would he come down on?
Posted By: rmiell Re: Inspectors strange interpretation - 01/14/03 03:06 AM
Why on both sides? Doesn't 1/2" sheetrock provide a 15 minute rating? Or is it 3/4"? Either way, if this rated material meets the requirement of a 15 minute barrier, anything on the other side has no effect.

Rick Miell
Posted By: HotLine1 Re: Inspectors strange interpretation - 01/16/03 01:13 AM
Clue me in guys:
Quote from above:
"He tells me there is an inspector in this area, who says, when using NM in a commercial building, the NM in attics and basements must be enclosed on both sides, within 15 minute finish rating in living area and attic or basement area."

Are we saying above that the ceilings must be 15 min. fire rated: and the "floors have to be 15 min fire rated also??

Or to put it another way:
OPen joist ceilings, or attic floors CANNOT have NMC wiring???

1/2" sheetrock is at least a 15 min fire rating. 2 layers of 5/8" make a 1 hour wall I believe. Tommorow, I have to ask the Building Inspector, and the Electric Sub-Code Official (Head Inspector) for clarifications.

John
Posted By: sparky Re: Inspectors strange interpretation - 01/16/03 09:35 PM
well good luck John,
somehow insinuating mc cable for residential wiring reeks of that steel tube institute's vengance on the 3 strory nm deal.... [Linked Image]
Posted By: HotLine1 Re: Inspectors strange interpretation - 01/17/03 03:31 AM
The clarifications will have to wait until Tuesday evening, as both gentlemen where "out" today, & I don't go back 'till Tuesday
John
Posted By: Roger Re: Inspectors strange interpretation - 01/18/03 01:06 AM
I hate it when somebody or an inspector uses (in their oppinion) the "thats not the intent" clause.

But in this case, the pure wording of 334.10{3}, IMO, is not the intent. [Linked Image]

Roger
Posted By: harold endean Re: Inspectors strange interpretation - 01/19/03 10:21 PM
I am reading the IAEI "Analysis of the 2002 NEC" book and on page 185 in reference to 334.10 it says "Type NM, Type NMC and Type NMS cables shall be permitted to be used in the following:

(1) One- and Two-family dwellings.

(2) Multifamily dwellings permitted to be of Types III, IV, and V construction except as prohibited in 334.12

(3) Other structures permitted to be of Types III, IV, and Type V construction except as prohibitied in 334.12. Cables shall be concealed within walls, floors or ceilings that provide a thermal barrier of material that has at least a 15-minute rating as identified in listings of fire-rated assemblies."


Does this help?
Posted By: sparky Re: Inspectors strange interpretation - 01/20/03 01:23 AM
a 15 min f-rating to protect the dwelling or the dwellings occupants??
Posted By: nesparky Re: Inspectors strange interpretation - 01/26/03 05:33 AM
The way I see it
(1) One- and Two-family dwellings.

(2) Multifamily dwellings permitted to be of Types III, IV, and V construction except as prohibited in 334.12

These are the residential type occupancies.
(3) Other structures permitted to be of Types III, IV, and Type V construction except as prohibitied in 334.12. Cables shall be concealed within walls, floors or ceilings that provide a thermal barrier of material that has at least a 15-minute rating as identified in listings of fire-rated assemblies."

These would be other than residential type ocupancies.
I would think that a finished drywall ceiling would solve the problem.
I would also let him fight with the GC.
Posted By: sparky Re: Inspectors strange interpretation - 01/26/03 01:27 PM
i agree,
said fire barrier of sheetrock bettween nm and occupant should meet the intent of the code, and i'd probably sic the GC on those whom are caught up in the literal wordage.