ECN Forum
Posted By:
jes
Panelboard Covers
-
01/09/03
07:05 PM
Other than the obvious issue of exposed live parts and 110-3(b)('99 Ed)...what Code sections would you cite for having to keep the covers installed on circuit breaker panelboards??
Posted By:
resqcapt19
Re: Panelboard Covers
-
01/09/03
08:20 PM
Look at 408.5 and 408.18.
Don
Posted By:
iwire
Re: Panelboard Covers
-
01/09/03
09:46 PM
OSHA 1926.403
Posted By:
Gwz
Re: Panelboard Covers
-
01/10/03
12:55 AM
Maybe a look at 527.2(A) should be considered also.
Temporary installation does not mean to be a hazardous working location.
©
ECN Electrical Forums