Posted By: elecbob 400 amp 120/208 v 3 phase service - 11/16/02 02:55 PM
I want to feed 2-200 amp 120/208 volt 3 phase panels from a 400 amp CT enclosure. The local utility does not allow me to install a second tap in the CT enclosure. Normally I would install a bus gutter and tap off there, but here I have a space restriction. A salesman at my wholesaler showed me some connection block that have a terminal rated for 500 KCM on one side and 2-4/0 on the other. The AL terminal is mounted on a plastic block and has plastic sides that interlock with other similar blocks.
Could I install 4 of these puppies in an 18' by 24' can rather than using a bus gutter? If It is allowed what are the minimum clearances from the sides of the can?
Thanks
Bob
Posted By: spyder Re: 400 amp 120/208 v 3 phase service - 11/16/02 04:11 PM
Do you have to use a CT cabinet? Why can't you use a standard 400 amp meter socket (320amp continuous and 400 amp intermitent)and use double barrel lugs on the load side connection?
Posted By: caselec Re: 400 amp 120/208 v 3 phase service - 11/16/02 06:05 PM
Elecbob

Do you want to tap off the load side of the C.T.'s for these 2 panels or are you trying to tap off the line side for 2 additional meters? Are there already load wires connected or would your 2 panels be the only load? I'm just trying to get the whole picture in my head.

Spyder - Do they make 3 phase class 320 meters?


Curt
Posted By: spyder Re: 400 amp 120/208 v 3 phase service - 11/16/02 06:20 PM
Its been a while but as far as I know they do.
Posted By: elecbob Re: 400 amp 120/208 v 3 phase service - 11/16/02 07:23 PM
Either 320 metering or 2 taps off the load side of the ct's is only allowed for residential here. This is commercial so no can do.I need 2-200 amp 3 phase panels. I need to make the tap outside the ct can.
I was wondering if there is an alternative to the bus gutter.
Thanks again.
Bob
Posted By: caselec Re: 400 amp 120/208 v 3 phase service - 11/16/02 07:55 PM
Bob

Are you saying that your utility does not permit parallel conductors on the load side of the meter for 400 amp services? It is pretty common to use two sets of 3/0 to feed a 400amp panel. For this project you would have the same number of cables in the CT cabinet but they would run to two separate panels instead of one panel.

Curt
Posted By: spyder Re: 400 amp 120/208 v 3 phase service - 11/16/02 08:40 PM
Is this a new service or an exisiting one/
Posted By: elecbob Re: 400 amp 120/208 v 3 phase service - 11/17/02 01:13 AM
Yes they allow parallel runs. But not to 2 seperate disconnects. This is a new service. Seattle City Light's meter division made the rule. A stupid one in my opinion.
Bob
Posted By: spyder Re: 400 amp 120/208 v 3 phase service - 11/17/02 01:38 AM
What about a 400 amp main switch and tap out of that to your two panels or set a 400 amp main distrubution panel. I realize both of these suggestions will add to equipment costs.
Ok, so you have a "space restriction" I imagen that is going under the CT. What I would do is put a 18x24 On the side of the cabinet and run 4" from the CT to the 18x24 and 2" pipe to each of the Panels.

Then into the 18x24 use four split bolts big enough to fit in The big wire and two of the 3/0 for the panels. and feed your Panels from that.

I've done this in the past, and found out that it will pass inspection and is more cost efficient.
Posted By: caselec Re: 400 amp 120/208 v 3 phase service - 11/17/02 07:23 AM
I agree that this rule does not make much sense. If they permit two disconnects and permit parallel cables what's the difference? Can you mount a 12 x 12 gutter above or below you 200 amp disconnects? If so run a set of 600's into the gutter and then tap off with 3/0's to each disconnect. Another way would be to have a single panel built with two 200 amp disconnects.

Jacuzzi Guy - You connected 3 wires in each split bolt? Where did you find split bolts rated for 3 wires?
Posted By: elecbob Re: 400 amp 120/208 v 3 phase service - 11/17/02 03:44 PM
Thank you very much guys. That's the info I was looking for.
This is a zero lot line building with an alley in back. There is an existing terminal can mounted on rhe alley side of the building at about 15 feet above grade. There is a 4 inch conduit from the utility's vault into the bottom of the can. The concrete floor of the building if 4 feet above the alley. City Light says we can't use the terminal can. They want us to dig down 7 feet (so we're 3 feet below alley grade) and install 2-4 inch conduits with 48 inch radius bends from the CT can to the alley. No LB's are allowed or we could do it differently. And they want us to pay about $7K for their work to extend the conduits into their vault.
Bob
Posted By: Bjarney Re: 400 amp 120/208 v 3 phase service - 11/17/02 04:25 PM
Isn't deregulation wonderful?