Posted By: DB Liquidetight Flex. Metal Conduit - 10/18/02 01:25 PM
After reading NEC 350.10 I believe there is no limit unless it is used for a service-entrance feed.

Now per NEC 356.12 the LFNC (non-metalic) is limited to 6ft.

Is there a lenght limit for LFMC (metalic)?
Posted By: resqcapt19 Re: Liquidetight Flex. Metal Conduit - 10/18/02 02:14 PM
In general there is no limit on the installed length of flexible wiring methods except for Flexible Metallic Tubing (Article 360) and types A and C of Liquidtight flexible nonmetallic conduit (Article 356). The other flexible wiring methods can be installed in unlimited lengths, subject to the 360° between pull points and the support rules for the raceway involved. Remember that in counting the degrees, every little variation from straight counts, and this will provide a limitation on the installed length.
Don
Posted By: DB Re: Liquidetight Flex. Metal Conduit - 10/18/02 03:15 PM
Thanks for the confirmation.
Posted By: walrus Re: Liquidetight Flex. Metal Conduit - 10/18/02 07:27 PM
Isn't the 6 ft rule only used when one is going to use the Liquid tite for bonding?
Posted By: spyder Re: Liquidetight Flex. Metal Conduit - 10/18/02 11:01 PM
I have even heard that there are guys out there wiring pool lights in Liquidtight Non-Metallic conduit. Has anyone heard the same?
Posted By: Joe Tedesco Re: Liquidetight Flex. Metal Conduit - 10/19/02 02:53 AM
Article 680 includes permission to use LTFNMC for a pool light.