If a conductor is for a continuous load and feeds the load through a raceway of more than three conductor, do you only apply the fill correction and forget the continuous load aspect. Or do you take them both into consideration?
Posted By: Bob Re: derate Q - 06/11/02 07:54 PM
You must use the derating for continous
load and conduit fill when derating these conductors.