Posted By: brownbagg breaker box location- code - 01/01/02 10:34 PM
What is the latest code on new construction breaker box location. I have heard so many different stories.
Posted By: Tom Re: breaker box location- code - 01/02/02 12:21 PM
Your panelboard will have overcurrent devices and therefore cannot be installed in locations exposed to physical damage, or in clothes closets, if residential cannot be in bathrooms. (220.24(C) & (D) & (E)

If the box contains a service disconnect & the installation is other than residential, can't be in a bathroom.230.70(A)(2)

Also, take into account working space requirements in110.34

Tom
Posted By: Redsy Re: breaker box location- code - 01/02/02 12:22 PM
Could you be more specific in your question? Are you referring to how near the point of entry a service disconnect must be, or in which loctions a panel may not be permitted?
Posted By: brownbagg Re: breaker box location- code - 01/03/02 01:38 AM
I have heard many different stories etc.
No closets.
No bathrooms.
Not behind doors.
Not close to gas water heater.
clear front entrances.

I want to put it in the laundry room across from washer and dryer but there a door problem. It will come close to falling behind the back door when open.