sharing circuits
-
12/07/01
02:25 AM
Is it legal to install a individual circuit such as a 240v 30a and put in 2 receptacles instead of one, if the loads would not be used at the same time?
Posted By:
Nick
Re: sharing circuits
-
12/07/01
02:41 AM
What you want to do looks code compliant per 210-21 and 210-23.
Posted By:
Steve Miller
Re: sharing circuits
-
12/07/01
10:47 PM
I know of nothing that says a 240v 30a ckt can only have one outlet. In a residence we normally only put one but that's because we need only one.
©