Posted By: Bill Addiss 210.52(D) 2002 NEC - 11/14/01 02:56 PM
How many Receptacles are needed when there are 2 sinks in a Bathroom?
Would 1 Duplex (GFCI protected) between them satisfy the rule? Or must it be 2 separate 'Outlets' as per definition?

What do you think?

Bill
Posted By: safari Re: 210.52(D) 2002 NEC - 11/14/01 03:34 PM
1 duplex between them would be sufficient as long as the sinks are less than 1800 mm appart and the receptacle is less than 900 mm from either.

tom
Posted By: Redsy Re: 210.52(D) 2002 NEC - 11/14/01 04:44 PM
Hi Safari.

Well, I guess the metric system has arrived!
Posted By: motor-T Re: 210.52(D) 2002 NEC - 11/14/01 06:30 PM
Bill;
One GFCI between would satisfy the code requirement for Bathroom gfcis, as long as no sink would be farther away from the outlet than 36 inches.
Posted By: sparky Re: 210.52(D) 2002 NEC - 11/14/01 09:15 PM
An outlet where one or more recetacles are installed

Ok, a regular GFI receptacle rates here ?is that the Q?
Posted By: Bill Addiss Re: 210.52(D) 2002 NEC - 11/14/01 11:07 PM
Thanks for the responses.

The question came up at a local Code Changes Seminar and the Instructor was saying that the intent here is for each sink to have it's own 'outlet'. An 'outlet' being defined as in Art 100 which means that a Duplex would only count as one.

Bill
Posted By: Bill Addiss Re: 210.52(D) 2002 NEC - 11/16/01 11:26 PM
Does everyone read this as meaning that a duplex would suffice between the sinks?

Bill
Posted By: Elzappr Re: 210.52(D) 2002 NEC - 01/15/02 06:54 PM
Just going over old queries and found your questions, Bill. I agree (or interpret) that one duplex is all that is required..no matter how many sinks, as long as it is within 3'of each sink's edge. Your workshop instructor was mistaken. All that is necessary is that someone can plug in some bathroom appliance without using an extension cord, since the appliance cords can't be longer than 3'.
In reality, the Code wording results in two receptacles (one for each sink), since the wall space between the sinks is usually pre-empted by the mirror.

[This message has been edited by Elzappr (edited 01-15-2002).]
Posted By: johngeorge Re: 210.52(D) 2002 NEC - 01/16/02 12:01 AM
I don't see how anyone can figure that this article requires an outlet for each sink. Must stay up nights conjuring these evil thoughts.
Posted By: Bill Addiss Re: 210.52(D) 2002 NEC - 01/16/02 01:01 AM
Elzappr,

Where does it say that appliance cords can't be longer than 3 feet? I think that people would have a very hard time with hair dryers. [Linked Image]

johngeorge,

I think I remember hearing him say that this was discussed at an IAEI meeting (in Mass?)Can anyone either confirm or deny that?

Bill
Posted By: sparky Re: 210.52(D) 2002 NEC - 01/16/02 01:19 AM
I believe the commentary supports the posters views here.....

(D) Bathrooms. In dwelling units, at least one wall receptacle outlet shall be installed in bathrooms within 900 mm (3 ft) of the outside edge of each basin. The receptacle outlet shall be located on a wall or partition that is adjacent to the basin or basin countertop.
Handbook Commentary..
Section 210.52(D) requires one wall receptacle in each bathroom of a dwelling unit to be installed adjacent (within 36 in.) to the washbasin. This receptacle is required in addition to any receptacle that may be part of any luminaire or medicine cabinet. If there is more than one washbasin, a receptacle outlet is required adjacent to each basin location. If the basins are in close proximity, one receptacle outlet installed between the two basins might satisfy this requirement. See 410.57(D), which prohibits installation of a receptacle inside bathtub and shower spaces. See Exhibit 210.9 for a sample electrical layout of a bathroom.
Section 210.11(C)(3) requires the receptacle outlets to be supplied from a 20-ampere branch circuit with no other outlets. However, this circuit is permitted to supply the required receptacles in more than one bathroom. If the circuit supplies the required receptacle outlet in only one bathroom, it is allowed to also supply lighting and an exhaust fan within that bathroom. This receptacle is also required to be GFCI protected according to 210.8(A)(1).