Posted By: lousen Generator disconnect - 10/29/01 01:17 AM
Does a gen.set located 80 ft. from bldg.require a disconnect where branch circuit conductors enter bldg.? Gen. set has 600 amp. breaker on unit.
Posted By: frodo Re: Generator disconnect - 10/30/01 12:33 AM
hi,
yes.
-regards

frodo
Posted By: Frank Cinker Re: Generator disconnect - 11/03/01 12:14 PM
Just for general information if located within 50 ft. disconnect would not be required. 2002 NEC. 700.12(B)(6). http://www.geocities.com/cinkerf/untitled.jpg