Does anyone know of a listed bonding fitting to connect conduit to a cable tray?
I believe Crouse-Hinds has such a fitting. When I go in tomorrow, I'll get the model #.
What we do is........
Install a bonding bushing on the end of the conduit. Jumper with #6 bare from the bonding bushing to a lug bolted to the rail of the tray. Fasten the conduit to the tray with a U-bolt clamp.
GJ
Crouse-Hinds "LCC Series" Cable Tray Conduit Clamps. Page # 5F-19 of 2000 catalog.
Redsy,
Thank you that was the one I have been looking for. Tmon