Posted By: doc 110-16 and 384-3 or 4 - 06/30/01 01:58 AM
I dont have my book so be kind here if im wrong on articles but 110 deals with clearance issues and 384 says that 25 ft above panels is to contain nothing but electric equipment,now do i understand that if u have a breaker panel or a panel board that u cannot run anything above it unless it is electrical we are running a steel conveyor about 8-10 ft above a 200 amp breaker panel
Posted By: sparky Re: 110-16 and 384-3 or 4 - 06/30/01 10:26 AM
doc;
110-26(f) mentions 384
110-26(f)(1)(a) EX, talks about foreign systems
which is defined in (b), as long as U provide protection from condensation,leaks or breaks your conveyor can stay.
Posted By: doc Re: 110-16 and 384-3 or 4 - 07/13/01 02:53 AM
sorry to be so long getting back but sparky would you take another look at these codes one talks about working area and the other is dedicated space and I see nothing about water it says nothing but electrical is allowed above it am i still missing something I have a book by Mike Holt understanding the code and it shows this area to be left open now what am i missing
Posted By: George Corron Re: 110-16 and 384-3 or 4 - 07/13/01 02:59 AM
Doc,
I don't think you are missing anything. clear space is clear space, NOTHING goes above that panel except electrical equipment. The purpose was for the electrician to always have a path to the panel, conveyors would be in the way, sorry, in my jurisdiction, down it comes.
Posted By: Anonymous Re: 110-16 and 384-3 or 4 - 07/13/01 04:39 AM
How about if he just suspends a slab of concrete there so the conveyor is on the next floor up in the building?