Posted By: Steve T 600-42 - 05/21/01 09:40 PM
What are the electrodes referred to by this section?

I looked at a connection of a neon sign with the leads from the tubing connected to the leads from the transformer secondary by twisting and tape around the connection with a rubber boot over the connection. Is this acceptable?
Posted By: Scott35 Re: 600-42 - 05/22/01 12:15 AM
Hi Steve T [may I call you Mr. T?? [Linked Image]],

Pretty sure the term Electrode is in reference to the Cathode of the Neon tube [the ends of the tube with the squiggly little wire inside and a thin bare wire coming out].

Have seen the type of connections you described many times before, but if that's compliant I have no idea - it seems to be OK as far as I am looking at it [don't like getting near 12-15KV!!... just a little humor].

Today, the sign vendor's crew was installing the transformers for the 2 new Wash. Mutual signs, so I got to grab a few documents that came with the transformers - mostly in regards to ground fault protection and KV per lamp lengths, diameter and color - vs - milliamps.

Scott SET