Posted By: Yoopersup Large Generator Grounding 480/277 V - 08/29/18 04:55 PM
Grounding requirements & Sections.

SDS & Non SDS .
Posted By: gfretwell Re: Large Generator Grounding 480/277 V - 08/29/18 10:14 PM
The biggest difference between SDS and non SDS is whether you bond the neutral (transfer equipment switches the neutral). Otherwise I think you just create a 250.grounding electrode system based on the largest ungrounded conductor ... but that is just off the top of my head.
Posted By: gfretwell Re: Large Generator Grounding 480/277 V - 08/30/18 12:08 AM
Looking at the code you get to 250.20 that talks about how you ground a SDS connected generator. If it is a non - SDS (unswitched neutral), there are no grounding requirements beyond the 250-122 EGC from the attached service.

From the handbook
Non SDS

[Linked Image from gfretwell.com]

SDS

[Linked Image from gfretwell.com]

If you do have an SDS it takes you to 250.30 that points you to 250.66 for the details of the GEC 250.52 for the electrode etc.
Posted By: HotLine1 Re: Large Generator Grounding 480/277 V - 08/30/18 06:55 PM
Greg:

Nice explanation!!
Posted By: gfretwell Re: Large Generator Grounding 480/277 V - 08/31/18 06:00 AM
Thanks, we do lots of generators around here so it is a common question. I usually tell homeowners looking to have transfer equipment installed that, if this is a manual system, the listed panel interlock is usually the best way to go. The labor will be much less and the part, although ridiculous for what you get, is still pretty cheap.
The only thing they really need is a vacant double slot in the panel and moving some breakers around to get your backfed breaker next to the discionnect. You then have to be sure they lift the bonding jumper in the generator to get circuit current off the EGC. This will not be an SDS.