Posted By: wewire2 Clothes Closet Fixture Clearance - 09/23/14 06:24 AM
When installing fixtures in clothes closets I have always considered the horizontal distance from the face of the fixture to the shelf when determining the clearance from the "nearest point" of storage space. Since the intent is to keep hot fixture parts from contacting or falling on storage items it seems that clothes hanging from a pole would infringe on the intent of the code but they most likely, measured diagonally would meet the clearance requirements. Are the parts supposed to be cool enough by the time they reach the clothes? What exactly is the definition of storage space since a clothes closet could be jam-packed?
Posted By: HotLine1 Re: Clothes Closet Fixture Clearance - 09/23/14 01:52 PM
wewire2:

From 2014 NEC...
410.2 Definition.
Closet Storage Space. The volume bounded by the sides
and back closet walls and planes extending from the closet
floor vertically to a height of 1.8 m (6 ft) or to the highest
clothes-hanging rod and parallel to the walls at a horizontal
distance of 600 mm (24 in.) from the sides and back of the
closet walls, respectively, and continuing vertically to the
closet ceiling parallel to the walls at a horizontal distance of
300 mm (12 in.) or the width of the shelf, whichever is
greater; for a closet that permits access to both sides of a
hanging rod, this space includes the volume below the
highest rod extending 300 mm (12 in.) on either side of the
rod on a plane horizontal to the floor extending the entire
length of the rod. See Figure 410.2.
410.

My opinion is that the fixture is to be far enough away from any combustible materials that could be ignited by the heat generated from the fixture. The 'hot' parts that you refer to are supposed to be contained by the fixture, as bare bulbs are not allowed.

And yes, I have seen some really 'packed' closets, and some really scary means of illumination.
Posted By: renosteinke Re: Clothes Closet Fixture Clearance - 09/23/14 03:01 PM
Observed abuses aside .... and anything can be abused .... the code does provide for specialty luminaires to be installed closer to stored materials than you might expect from the excerpt posted above.

For example, there exist illuminated closet rods that, by their design, can't help but place the cloths much closer to the light than 12".

I expect hat with the expanding use of CFL and LED light sources, as well as the legislative assault on the old-fashioned incandescent light bulb, that closet lighting will soon stop being such a 'hot' topic.

Now, does putting an enclosed bulb, or a CFL bulb, into an ordinary fixture make that fixture either enclosed, or fluorescent, under the NEC? Good question.

Early on, the IAEI took the position that no, it does not. In a like manner, California took the position that such did not make the fixture energy efficient either. Both justified their positions in that you "might" later put an incandescent bulb in the fixture.

I do not see anything in the NEC, or the various energy codes, that allows for such an interpretation. Not only is such an approach an affront to our concepts of right and wrong (do we ban cars because they MIGHT be used to commit crimes?), but Article 90 of the NEC makes it pretty clear that what 'might' happen in the future is beyond the scope of the code.
Posted By: HotLine1 Re: Clothes Closet Fixture Clearance - 09/23/14 06:14 PM
As Reno said, there are approved, listed alternative fixtures other than incandescent.

I've seen nice LED fixtures, about 6" round, surface mount that do a good job of illumination. Surface mount (over the door) fluorescents work also.

Posted By: wewire2 Re: Clothes Closet Fixture Clearance - 09/23/14 07:02 PM
Thanks for the help with the code reference. Forgot that was there and was looking in article 100. Brushing up on residential has actually been fun.
Posted By: HotLine1 Re: Clothes Closet Fixture Clearance - 09/24/14 01:24 AM
Remember, we areall students of the NEC....
Posted By: gfretwell Re: Clothes Closet Fixture Clearance - 09/24/14 05:46 AM
The actual clothes closet rules are 410.16

I had one of the LED proposals that were rolled up into that code change (accepted in principle) 410.16(C)(5)

Quote
410.16 Luminaires in Clothes Closets.
(A) Luminaire Types Permitted. Listed luminaires of the following types shall be permitted to be installed in a closet:
(1) A surface-mounted or recessed incandescent luminaire with a completely enclosed lamp
(2) A surface-mounted or recessed fluorescent luminaire
(3) Surface-mounted fluorescent or LED luminaires identified as suitable for installation within the storage area
(B) Luminaire Types Not Permitted. Incandescent luminaires with open or partially enclosed lamps and pendant luminaires or lampholders shall not be permitted.
(C) Location. The minimum clearance between luminaires installed in clothes closets and the nearest point of a storage space shall be as follows:
(1) 300 mm (12 in.) for surface-mounted incandescent or LED luminaires with a completely enclosed light source installed on the wall above the door or on the ceiling
(2) 150 mm (6 in.) for surface-mounted fluorescent luminaires installed on the wall above the door or on the ceiling
(3) 150 mm (6 in.) for recessed incandescent or LED luminaires with a completely enclosed light source installed in the wall or the ceiling
(4) 150 mm (6 in.) for recessed fluorescent luminaires installed in the wall or the ceiling
(5) Surface-mounted fluorescent or LED luminaires shall be permitted to be installed within the storage space where identified for this use.
Posted By: wewire2 Re: Clothes Closet Fixture Clearance - 09/27/14 07:27 PM
Looks like the trouble is finding LED fixtures identified for use in the storage space. Wonder how much it would cost the manufacturer to get this extra rating.
Posted By: gfretwell Re: Clothes Closet Fixture Clearance - 09/27/14 07:44 PM
I think this will start showing up more as the LED luminaires get more popular. If you are paying for the listing anyway, adding the endorsement for storage space is just a small incremental cost in the grand scheme of things. As the NRTLs get comfortable with the idea this should be a fairly simple test beyond what they do for any product and that is pretty extensive.
They blow things up in every conceivable way to see how they fail but even with that, I am amazed at some things that pass.
Posted By: wewire2 Re: Clothes Closet Fixture Clearance - 09/29/14 02:01 AM
I'm amazed at what passes also. For instance, some of the weatherproof boxes and LB's I've used lately seem like they were designed to strip the insulation off the wire when it's installed. Ground screws strip out. Total junk.
Posted By: gfretwell Re: Clothes Closet Fixture Clearance - 09/29/14 06:26 AM
I had a picture of one of those LBs here a while ago. There was a sharp shoulder on the inside of the hubs that you could strip wire with.
Posted By: ghost307 Re: Clothes Closet Fixture Clearance - 09/30/14 02:59 PM
I got disgusted with UL a few years ago when I saw a design flaw in an MCC starter.

The operating mechanism for the fused disconnect blocked access to the fuse holders. The only way to change the fuses was to turn the starter disconnect ON and change the fuses while hot. I mentioned this to the guy at UL and he told me that they only test for safety when properly installed and were not interested in anything having to do with "maintenance".

I now consider the UL Listing as little more than a starting point when I'm deciding what to specify on a job.
Posted By: sabrown Re: Clothes Closet Fixture Clearance - 10/01/14 12:10 AM
This creates a major conflict, allowing a listed device to be installed specifically in conflict with the code. I do not have an issue with the LED rod lights and their conflict, but I know of another case where equipment is "Listed" and if installed according to listing, it works, but the manufacturer then says on the side that you don't need to follow code because our device is better than code, which is a lie or at best a horrible misrepresentation and creates a large hazard. The mfg. tried to get code changed, but the scientific community stopped it and still after many proofs of the failure of the device when installed according to the manufacturer claims, they misrepresent on.

Shane
Posted By: ghost307 Re: Clothes Closet Fixture Clearance - 10/01/14 11:08 PM
It's up to the AHJ if they want to waive a Code requirement, but personally I would not accept a claim of a manufacturer as sufficient to ignore the Code (which, once properly adopted, has the force of law).