Posted By: Yoopersup Amp draw 650 HP Mtr. - 09/21/12 08:26 PM
650 Hp Mtr. 575volt 3 phase.
Requires 480v we have .
/575 buck boost to run.
Questions??
Current draw on 480v side??
Current on 575 side side ??
Mtrs coming in from Canada as we run mostly 480 in USA we're running into this more often.
Posted By: Yoopersup Re: Amp draw 650 HP Mtr. - 09/24/12 06:11 PM
???????
I can't believe I'm the only one that works with this stuff?????
We Have 480 3 Phase
The motors coming in 575 Volt
We need Buck Boost Transformer.
Amp draw Pri. Of buck boost (480)
Amp draw Sec, of buck Boost (575)
Breaker size on Pri. to hold Mtr starting on Secondary.
Posted By: gfretwell Re: Amp draw 650 HP Mtr. - 09/24/12 06:17 PM
Deeper water than I ever swam in wink

What is that driving?
Posted By: sparkyinak Re: Amp draw 650 HP Mtr. - 09/24/12 09:51 PM
I'd would work with a supplier and have them size it and if it don't work, its on them. I just read too that VFD's can be used as softstarters too and give the motor flexibility where a softstarter can't
Posted By: twh Re: Amp draw 650 HP Mtr. - 09/25/12 02:05 AM
I haven't worked with a buck/boost transformer, but the relationship between voltage and current is inverse. It can't be anything else unless you have a pit where the extra va go. You need the flc of the motor. You probably need to size the transformer with the same factor as the conductor size. Does that help?
Posted By: HotLine1 Re: Amp draw 650 HP Mtr. - 09/25/12 02:13 AM
Yoop:
Your best bet would be to hunt down a electrical 'power' engineer.

Maybe Scott35 will jump in here on this, but I'm in with Greg...that water is much to deep.

Looking at 430.250, I would take a stab at an FLA of 800 amps @ 480 and 640 @ 575. Just using an approx 20% diffeence from 480 to 575.

Could you not use a 480 primary, 575 secondary transformer, instead of a buck/boost.

Posted By: Scott35 Re: Amp draw 650 HP Mtr. - 09/25/12 01:36 PM
Yoop,

What is the FLA of the Motor at 575V?

Use the KVA input rating of the Motor to configure the Transformer size and input FLA at 480V.

Your Voltage Increase will be 95 Volts (575 - 480 = 95), so a standard "Buck-Boost" type Transformer is not an option; the highest Secondary Voltage I know of is 48V.

An Autotransformer (pre-wound), or typical Isolated Transformer (575V to 480V Closed or Open Delta) arrangement may be needed.

Anyhow, obtain the FLA at 575 Volts to obtain the Motor's Full Load KVA, which may be converted to Transformer Capacity and Motor FLA at 480 Volts.

Example:
If the 650 HP Motor's Nameplate FLA is 640A at 575V, the KVA will be 637.44 KVA (637,440 VA)
At 480V, the FLA becomes 767.08 Amps.
The Transformer will require a Secondary with 750 KVA Capacity.
For a Buck-Boost with 95 Volt Secondary, that would result in 150 KVA capacity - as either:

1: For an Open Delta arrangement: 2x 75 KVA,
2: For a Wye arrangement: 3x 50 KVA

You might obtain (2) Single Phase 480V x 120V Transformers in 100 KVA Capacity, which you could configure in an Open Delta Network. This arrangement will result in 600V output.
Each Secondary will need to be rated at least 76.8 KVA (120V x 640 Amps = 76,800VA).

Good luck!

-- Scott (EE)
Posted By: HotLine1 Re: Amp draw 650 HP Mtr. - 09/25/12 06:50 PM
Scott:
That's clear as a bell! Thanks from me to you!
Now, Ernie....it's up to you.
I'm curious to see if my 'guesstamate' was close.
Posted By: Yoopersup Re: Amp draw 650 HP Mtr. - 09/26/12 01:53 AM
Its for a Mining Drill bore.
Let ya know what was done when its decided/
Just Kinda wondering if its hooked to a Buck/Boost.
Would it draw the same on the 480Volt side of the Buck Boost
as if it was running on 480 not 575.
I've run 575 mtrs on 480 before but never this Big.
Posted By: Scott35 Re: Amp draw 650 HP Mtr. - 09/29/12 06:34 PM
John;

Quote

That's clear as a bell! Thanks from me to you!


Cool! Thanks for the nice words!

Yoop;

Quote

Just Kinda wondering if its hooked to a Buck/Boost.
Would it draw the same on the 480Volt side of the Buck Boost
as if it was running on 480 not 575.


Input KVA will match the Output KVA, per the Motor's Load.

i.e.: If the Motor is producing 100 HP, on the 460V Input side, the load would be 123.7 Amps, and the Apparent Power input would be 98.82 KVA.
On the 575V Output side, the Motor would be drawing 99.2 Amps, and the Apparent Power output would be 98.82 KVA.

-- Scott (EE)
Posted By: sparkyinak Re: Amp draw 650 HP Mtr. - 11/07/12 08:48 PM
In a class down here in Dallas. A classmate is talking about a scrap car grinder that is 7000 hp (not a typo)
Posted By: ghost307 Re: Amp draw 650 HP Mtr. - 11/08/12 04:17 PM
We just bought a new VFD for a 3,750Hp motor for a water pump.
The manufacturer's test facility had a 6,000Hp motor that they used for their equipment testing...and they were getting ready to install the new 12,000Hp motor that they ordered so they could test "the big stuff".

Yikes!!
Posted By: LarryC Re: Amp draw 650 HP Mtr. - 11/11/12 03:26 AM
I wonder what they connect to the motor to simulate the mechanical load?