Posted By: HotLine1 What say ye?? - 05/14/11 02:56 AM
Residential PV grid-tie; <12KW:

Could Article 705.21 (2008 NEC) be cited to require a disconnect on PV (solar) inverter output to grid-tie.

In other words a disconnect to remove solar AC from backfeeding into the utility grid?

And....what says it should be outside, on exterior of resi??

Posted By: gfretwell Re: What say ye?? - 05/14/11 07:00 AM
Grid tie inverters will not run without the grid being present. I am not even sure they have the 60hz time base to make power without the grid (they use the grid to pace the inverter?). I assumed that was why they wouldn't put out.

This is the impression I got from the people trying to sell me a system anyway. I did want off grid generation in an outage and they said not with a grid tie inverter.

This is one of those things I would fall back to the manufacturer's instructions on. They know what their box is supposed to be able to do.
I am not sure if this is part of the listing standard.
Posted By: gfretwell Re: What say ye?? - 05/14/11 07:20 AM
The white book wasn't much help QIIO says basically "install it using the instructions" and the grid connect inverter part throws you back to the off grid inverter section so it does appear that how this shuts down is not part of the listing standard.
Posted By: renosteinke Re: What say ye?? - 05/14/11 03:33 PM
It is my impression that the units are designed to back-feed a breaker in the panel, and this serves as your disconnect.

I'm not completely happy with this as the only disconnect - I'd like an 'off switch' and OCPD at the collector panel as well - but that's another matter.
Posted By: LarryC Re: What say ye?? - 05/14/11 07:42 PM
I wonder if the manufacturers of grid tie inverters have have models that can change between grid tie and non grid tie by means of an external contact. That way, when the inverter is connected to the grid it can backfeed. When the grid goes away, a contact on the grid fed isolation switch allows the inverter to restart and power up local loads up to the capacity of the inverter.

Other choice would be a large UPS backed up by the PV and battery system.
Posted By: Tesla Re: What say ye?? - 05/14/11 10:11 PM
Larry C

My understanding is that EUSERC policy excludes the installation of any such scheme.

Renosteinke

Out my way the inverter has to be co-located VERY close to the panel.

EUSERC utilities insist upon such. The idea is that upon the event of fire/ wiring faults the first responders can kill the power source with no more than two throws.

EUSERC is not at all concerned about anyones desire to have partial power when the grid goes down. Their concern is their own employees. Having studied the issue at some length it has been resolved that it's their way or no power for you!

It is futile to try and jigger around their scheme. Once any such contraption is discovered the spanking will be too severe to bear.
Posted By: gfretwell Re: What say ye?? - 05/14/11 10:37 PM
The subsidy went away so I put my solar plans on hold but I had decided that I would put transfer equipment in and use 2 inverters if it came to it.
I did wonder if you could "tickle" the grid tie inverter with a regular 12v inverter to light it up after the real grid was switched away. I am just guessing but I suspect the solar inverter looks for voltage coming in on the utility side at each zero crossing and does not gate the solar inverter if it doesn't see something. I suspect the problem would be that your 12v inverter could not push into the attached load hard enough to get things started.
The real answer would probably be 3 pole transfer equipment switching both phase legs and the DC output to a non-grid tied inverter.
Posted By: renosteinke Re: What say ye?? - 05/15/11 12:19 AM
Tesla, your understanding of EUSERC rules must be flawed.

UL has already listed a number of 'micro inverters.' These are located at the solar panel; several can combine their outputs into a single feeder to a back-fed breaker at the panel.


It's not so much trying to 'jigger around their scheme' as a matter of technology being out of step with technology. It doesn't help that 'policy' is partly driven by acolytes of "Green Religion."
Posted By: Tesla Re: What say ye?? - 05/15/11 09:59 PM
Yes, those units can be sold OUTSIDE EUSERC utilities.

In fact, there are no end of non-EUSERC UL listed products.

EUSERC prohibits many practices acceptable to the rest of the industry.

Posted By: gfretwell Re: What say ye?? - 05/16/11 04:37 AM
At a certain point the customer is going to exert some rights about what they can do on the load side if the meter. I am old enough to remember when the Telcos prohibited connecting anything to a phone line that they didn't rent you. That went away too.
I understand they need some standards of safety and the ability to protect the integrity of the grid but we can't let them get silly here.
Posted By: harold endean Re: What say ye?? - 05/16/11 01:27 PM
I have seen where the PV installers would put them on the outside of the house. They called it "utility disconnect". Then that practice stopped.
Posted By: harold endean Re: What say ye?? - 05/16/11 01:30 PM
If you have the PV systems with the built in inverters on the panel, every night time (theoretically) the PV power would be disconnected from the Poco grid. That would be on the outside of the house. To me that is the safer install.
Posted By: HotLine1 Re: What say ye?? - 05/16/11 07:06 PM
Gentlemen:

Back to my original quest please....

Our utility was requiring an AC disconnect (lockable) to isolate PV from the grid.

They (POCO) can no longer mandate it due to jurisdictional issues.

Can it be mandated via 705.21 without consideration of the inverter output being dependent on grid voltage???

Posted By: Vindiceptor Re: What say ye?? - 05/16/11 08:20 PM
Can you explain the 'jurisdictional' issue that prevents the POCO from requiring the PV disconnect?

I would like to know how the POCO can be cutout of the decision to safely isolate the grid from the PV source. I have worked with all three major Calif utilities (SDG&E, SCE and PG&E) plus a couple of smaller ones (SMUD and SVP) and have yet to find one that would allow the interconnection without a visible blade, lockable PV disconnect.

While I agree it is not really necessary given the inverter's required anti-islanding features 'anything' can fail (including the anti-islanding features) and for their piece of mind they mandate the visible verification within their Rule 21 requirements.

I believe 705.21 could be referring to the AC switch required to meet 690.15 and 690.17, those switches are usually integral to the inverters and would not meet the Utilities 'visible' requirement nor would a circuit breaker in Calif since you can not 'visually' ensure the circuit is open.

I should note that I don't do RESI work, so what passes the AHJ's and Utility's inspections in that regard I can't comment on.

As far as being outside, I believe it's not required, but if it isn't and it's not adjacent to the Utility disconnect then a plaque would need to be provided at each disconnect (Utility and PV) showing the location of each per 230.2(E)
Posted By: HotLine1 Re: What say ye?? - 05/16/11 09:16 PM
Vin:
The only reason I was presented was 'not within the POCO tarrif'.

I have a email into the BPU to see if they have any reasons, but for now that's all I have.

Posted By: gfretwell Re: What say ye?? - 05/16/11 11:13 PM
Quote
Means shall be provided to disconnect power production equipment, such as utility interactive inverters



You need some kind of disconnect but I assume there is one in the inverter. When you say "lockable", that is the part that is not in 705.21.
Posted By: Vindiceptor Re: What say ye?? - 05/16/11 11:34 PM
Originally Posted by gfretwell
You need some kind of disconnect but I assume there is one in the inverter. When you say "lockable", that is the part that is not in 705.21.


The thing that negates most all inverter integral disconnects as being acceptable to the Utility is the "visible blades" part, very few of them have this feature and a circuit breaker is also unacceptable.

Most inverter do have lockable disconnects of some sort, but lack the visual part so they can't tell if the device is actually opening the circuit.

Anything out here over 30kW will be turned down immediately without this feature. The small Solectria inverters (10-95kW) are the only ones I know of that comply and that's only because they just tack off-the-shelf disconnects onto their inverters.
Posted By: HotLine1 Re: What say ye?? - 05/17/11 12:54 AM
Greg:

Removing the term 'lockable' from my question, would you then agree that 705.21 could be cited?

Posted By: gfretwell Re: What say ye?? - 05/17/11 04:05 AM
That certainly means you need a disconnect.

That gets further defined in 22

Quote
705.22 Disconnect Device.
The disconnecting means for ungrounded conductors shall consist of a manually or power operable switch(es) or circuit breaker(s) with the following features:
(1) Located where readily accessible
(2) Externally operable without exposing the operator to contact with live parts and, if power operable, of a type that could be opened by hand in the event of a power-supply failure
(3) Plainly indicating whether in the open (off) or closed (on) position
(4) Having ratings not less than the load to be carried and the fault current to be interrupted. For disconnect equipment energized from both sides, a marking shall be provided to indicate that all contacts of the disconnect equipment might be energized.
Posted By: HotLine1 Re: What say ye?? - 05/17/11 04:12 AM
As always, I thank you!!!