ECN Forum
Posted By: peanutmydog What Nec codes saids? - 09/29/10 01:28 AM
what is the closes that a receptalce can be to a remote gas pump?
Posted By: gfretwell Re: What Nec codes saids? - 09/29/10 07:44 AM
Is this a "pump" or a "dispenser". The difference is the width of the class 1 div 2 area.
If this is outdoors, a safe answer is 3 feet or greater away, 18" or greater above grade ... If I am reading Table 514.3(B)(1) right. Underground raceways still need sealoffs.