Posted By: Merlin 400 amp 3 phase 120/240 question. - 01/18/10 01:10 AM
According to 310.15(B)(6), I can feed a 120/240 single phase service with 400 MCM copper. Am I correct that for a 4 wire, 3 phase, 120/240 service that I have to derated per 310.15(B)(2)(a)? If so, I would need 500 MCM, correct? Thanks, Merlin
Posted By: sparkyinak Re: 400 amp 3 phase 120/240 question. - 01/18/10 01:26 AM
310.15(B)(6) is for single phase dwelling units service and feeders. Since that you are bringing in a 3 phase service, you can not derate. If you were to then run single phase feeders to like apartment units, those could be derated. Otherwise no derating is allowed.
Posted By: Merlin Re: 400 amp 3 phase 120/240 question. - 01/18/10 01:33 AM
Thanks Sparky. So if that is the case, then I have to run 500 MCM conductors then. Correct?
Posted By: sparkyinak Re: 400 amp 3 phase 120/240 question. - 01/18/10 01:51 AM
yep
Posted By: sparkyinak Re: 400 amp 3 phase 120/240 question. - 01/18/10 02:03 AM
I stand corrected, yes as far as your original yes. The service wires by code are only required to be big enough to the load caulated in Article 220. However if you are building something off of an engineer's drawing, you need to use was was spec'ed of do a RFI with the designer of record. There may be also local ordinaces. I typically size my feeders based on my main breaker size. This way if the loads increase on the future, the customer will not have to pay twice.
Posted By: Merlin Re: 400 amp 3 phase 120/240 question. - 01/18/10 02:12 AM
Am I allowed to size according to breaker size at 80%? Therefore allowing me to use 350 MCM. Or would I have to use 100% rating? Thats how I read the code one minute, but the next I'm second guessing myself!
you can run at 100% however if you going to make single phase feeder network you can not reduce the neutal conductor at all espcally feeded from 3Ø supply.

Merci,Marc