Posted By: Yoopersup Article 620 Elevator Machice Rooms. - 03/05/09 04:06 PM
The way I read it No Electrical Panels or Electrical Equipment other then required to power or Control the elevator is allowed in this room.
Example (Main Electrical SERVICE Panel). (Not Allowed )
Panels or Disconnect Switches for feeding Elevator Equipment or Mtrs (Allowed).
Posted By: renosteinke Re: Article 620 Elevator Machice Rooms. - 03/05/09 05:08 PM
Article 620 is subservient to the non-NFPA "Elevator code." I have NOT read this other code, so I cannot place the article in context.

Does anyone have a link, or a copy?
Posted By: Yoopersup Re: Article 620 Elevator Machice Rooms. - 03/05/09 06:14 PM
Called The State Elevator inspector. He said Yep nothing in there that does not pretain the the Elevator Equipment.
Thanks
Posted By: HotLine1 Re: Article 620 Elevator Machice Rooms. - 03/06/09 01:11 AM
Only equipment associated with the elevator. (Period)

Posted By: sparkyinak Re: Article 620 Elevator Machice Rooms. - 03/07/09 05:09 AM
John hit it on the head. Only elevator related equipment is allowed. ANS1 17.1 is a common Elevator Code to go by. What it really gets fun is fire detection, and sprinklers in the shaft.