Posted By: wb007 arc fault circuits required in nec 08 code - 02/10/09 04:33 AM
Are they required on just outlets (recept)in the described locations or on lighting outlets too.(ceiling fixture /recess lites) also is their any exception for single outlets for a cellar applance...
#1) Welcome to the forum! nice to have another 'Bay stater' here!

210.12, Has been accepted in it's entirety. As of 24.00/1-1-2008.

ALL 120 Volt, single phase, 15 and 20 AMP ckts..

"Lighting outlets"-- answered your own question.

Yes.