Posted By: sokoservices NEC 2002/ 2005 question on Motors - 11/19/08 05:14 AM
Hello all.
Please help me pass my exam.
One question that I cant seem to find is:
" What is the maximum distance for flexible cord feeding a motor?"


Please help!

thank you

Posted By: gfretwell Re: NEC 2002/ 2005 question on Motors - 11/19/08 06:02 AM
680.21(A)(5) says pool pumps, cord and plug connected can only have a 3' cord.
Posted By: leland Re: NEC 2002/ 2005 question on Motors - 11/19/08 06:47 AM
422.16(B)(2).
422.16(B)(2)(2)
422.16(B)(4)(2)
430.42(C)
680.7(A)
680.21(A)(5)

Heres a few, check them out and you decide the common denominator.

Some think I'm nuts...But I enjoy danceing around the book.
(Thats not why they think I'm nuts though)

When looking for an answer: Focus on the "key" word. Here Flex. cord...422.16. Next "MOTOR" Start at 430 then move from there. You'll be surprised!!!

Best of luck!!!!
Posted By: gfretwell Re: NEC 2002/ 2005 question on Motors - 11/19/08 09:27 AM
It is really a bad question.
I guess the real answer they are looking for would depend on what the options they give you on the test.
So far we have found 36" (pools), Between 3' and 4' (dishwashers) and 18" (disposals & range hoods).

I picked on 680.22 because that is the only article that specifically says "motors" and lists a length.
Appliances may have motors in them but that is not the way the article is worded.

Posted By: sokoservices Re: NEC 2002/ 2005 question on Motors - 11/19/08 12:49 PM
The answer that they want me to use it 6'. I am not sure where they would have gotten that answer. I am still looking.
Posted By: gfretwell Re: NEC 2002/ 2005 question on Motors - 11/19/08 06:21 PM
That sounds more like the rule for spiral armor wiring methods ref grounding ... unless you are in Chicago.
Posted By: leland Re: NEC 2002/ 2005 question on Motors - 11/23/08 06:34 PM
Not to 2nd guess..But do they specifically ask "cord"?
6' seems to be more of a "flex" issue,greenfield etc. In wich case 6' jumps out, GEC in any piece longer than 6' etc..
I can't find 6' anywhere associated with "cord connected.."
Posted By: sokoservices Re: NEC 2002/ 2005 question on Motors - 11/25/08 09:52 PM
The question says CORD but i am with you all i can find is the section about the 6' flex cable (greenfield/ mc)
Posted By: Yoopersup Re: NEC 2002/ 2005 question on Motors - 11/27/08 08:26 PM
Any one look at Busways Article (368)>
Industrial 368.56(B)2
You can go a lot longer then 6 ft. The ist support is required within 6 ft .
2005Handbook page 407 shows a good example.

Also see 400.14 (50ft)