Posted By: gfretwell Loop in the code - 10/25/08 04:57 AM
Our Friend Bryan Holland (BHGravity) brought up an interesting conundrum in 210 over at his house.
We all know 210.11(C) Exception says we can have the fan and counter receptacles in a bathroom on the same circuit if that is the only bathroom served ... but since 2005 210.23(A) Exception says you can only serve "receptacles".

Makes you go Hmmm
Posted By: renosteinke Re: Loop in the code - 10/25/08 02:37 PM
Good catch!

Looks like homeowners aren't the only ones to confuse 'receptacles' and 'outlets.'

November fast approaches ... get that proposal in!
Posted By: leland Re: Loop in the code - 11/02/08 04:39 AM
Well, 210.23 (A) exception, refers you to 210.11 (C) ("..specified in that section.").
I would interpret that to make 210.11 the govorning rule,in this instance.(bathrooms)

Additionaly, most exhaust fans do have recepticals in the units. So don't wire the vanity light and switches.