Posted By: windmiller 13.8 kV Cable Installation - 08/18/07 09:42 PM
Is it permissable to install a 13.8 kV MC cable on the ground or does the cable have to be buried per 300.50 or does 300.37 allow this with MC cable?

Thank you,

Windmiller
Posted By: Yoopersup Re: 13.8 kV Cable Installation - 08/19/07 02:28 AM
328.10 & 328.12 Medium Voltage Cable

330.10b(4)MC uses primitted

300.37Requirements for over 600 Volts ,Nominal

Definitions read Exposed (as refered to un 300.37

My opinion No(must be underground or in a raceway or support system (tray) above ground. if subject to physical harm . Or Exposed to unqualified persons.