Motor Oveload Protection - 08/12/07 12:47 AM
I recently had a work-order for a motor that was periodically tripping it's overload. Small 480V pump motor with a FLA of 1.0 and a service factor of 1.0 At the time that I looked at it, it was drawing 0.9A on every phase.
The maintenance guy I was with wanted to crank up the adjustable protection on the OL relay, which was set at 1A but topped out at 1.6A. My answer was that given that the SF of the motor was only 100%, while it may stop the tripping overloads, it would seriously reduce the life of the motor. Since this motor has been in service for some time without previously overloading, and considering that this is an intermittant problem, my suggestion was some sort of mechanical restriction in the pump, and probably not an electrical problem.
According to code it seems I was wrong. I don't remember what the actual HP rating of the motor was, but I'm guessing, based on the FLA that it's more than 1HP. So, according to 430.32(A)(1), it would have been safe to set the OL protection to as much as 115%? Were the OLs just set a too close to the operating range of the motor?
As an aside, does anyone have a good tutorial for motor starters and overloads? In case it's not really obvious, I'm not too familiar with them. For example, why does it seem like every motor starter setup has two contactors? One that has the OL protection in it, and then one down-stream from that?
Also, 430.32(A)(1): Motors with a marked temperature rise of 40 degrees C or less can have an OL rated at 125% FLA. Why would you be able to increase the size of the OL protection on a motor that wasn't able to tolerate as much of a heat increase?
Sorry about all the questions, just trying to understand all this.
-John
The maintenance guy I was with wanted to crank up the adjustable protection on the OL relay, which was set at 1A but topped out at 1.6A. My answer was that given that the SF of the motor was only 100%, while it may stop the tripping overloads, it would seriously reduce the life of the motor. Since this motor has been in service for some time without previously overloading, and considering that this is an intermittant problem, my suggestion was some sort of mechanical restriction in the pump, and probably not an electrical problem.
According to code it seems I was wrong. I don't remember what the actual HP rating of the motor was, but I'm guessing, based on the FLA that it's more than 1HP. So, according to 430.32(A)(1), it would have been safe to set the OL protection to as much as 115%? Were the OLs just set a too close to the operating range of the motor?
As an aside, does anyone have a good tutorial for motor starters and overloads? In case it's not really obvious, I'm not too familiar with them. For example, why does it seem like every motor starter setup has two contactors? One that has the OL protection in it, and then one down-stream from that?
Also, 430.32(A)(1): Motors with a marked temperature rise of 40 degrees C or less can have an OL rated at 125% FLA. Why would you be able to increase the size of the OL protection on a motor that wasn't able to tolerate as much of a heat increase?
Sorry about all the questions, just trying to understand all this.
-John