Posted By: gfretwell Rumors of 2008 changes - 01/26/06 05:48 AM
I hear rumors 250.32(B)(2) may be going away and that 210.12(B) will expand to all 15 and 20a 120v receptacles (outlets?).
Posted By: Ryan_J Re: Rumors of 2008 changes - 01/26/06 02:24 PM
Regarding 250.32(B), that is true at this point in the game. I wrote the proposal, and talked with Mike Holt who sat in on the panel meeting with CMP 5.
Posted By: iwire Re: Rumors of 2008 changes - 01/26/06 10:38 PM
Ryan if you don't mind what was the safety reason for the change?

And of course my next question is if that practice is unsafe how can services be safe?

Bob
Posted By: Ryan_J Re: Rumors of 2008 changes - 01/27/06 02:37 PM
The safety reason for the change is that bonding enclosures with a cuurent carrying conductor is not a good idea.

Regarding services...if this passes I plan on submitting the same concept for services in 2011. Of course, services don't typically fall under the scope of the NEC, but as written now, you don't have the option of installing an EGC from the transformer and bonding it to the enclosure, and floating the nuetral at the service.
Posted By: gfretwell Re: Rumors of 2008 changes - 01/27/06 05:50 PM
That certainly sounds like a hard sell. You will need to coordinate this change with the NESC and I bet the utilities who sit on those CMPs will veto it.
I do see the value of the idea but I doubt the utilities will.
This is the kind of idea that needed to be established back when Edison and Westinghouse were deciding what the grid would look like.
It will certainly make me want some stock in Landis & Gyr and Thomas & Betts. They will have an instant market for a couple hundred million meter bases.
Posted By: Ryan_J Re: Rumors of 2008 changes - 01/27/06 06:02 PM
They can't "veto" anything. All they can do is vote against it.
Posted By: gfretwell Re: Rumors of 2008 changes - 01/27/06 09:10 PM
If the NESC CMPs are anything like the NEC CMPs they are packed with industry reps. If the industry doesn't want something it don't happen. On the other hand, if they have a product they are pimping it gets fast tracked to the front of the line, ready or not. I only have to point to 210.12 and products that were put in the code, in spite of the fact they didn't exist.
Personally I think the whole process is broken, bordering on being corrupt.
Posted By: pdh Re: Rumors of 2008 changes - 03/11/06 11:22 PM
bump...

Even I, a non-electrician, can see the safety advantage of not doing things as in 250.32(B)(2). I'd be happy to see that go away.

But as for 210.12(B) being expanded, I'd say we are not really ready for that, yet. We may not be for quite a while. But I do think we could live with it expanding provided that some better exceptions are made available, such as for dedicated circuits. Maybe it could be expanded to some additional areas of the home. Maybe an exception could be made for some areas (where cords are unlikely to be an added safety hazard) when AC, MC, or metallic conduit protects the wiring.

We could end up seeing a lot more AFCI breakers for sale on EBAY as homeowners end up doing their own replacements. What may be more influencial regarding this would be how homeowner insurance policies are written. If existance of AFCI protection is required for lower rates (and undocumented substitution discovered after a fire results in non-payment), then I can see more of this coming about. While I could imagine the insurance industry would back this change, I would think they could effect the change through their rate structures, too.
Posted By: aldav53 Re: Rumors of 2008 changes - 09/12/06 05:55 AM
I think they ought to do away with allowing wrapped ridgid underground in the 2008 code. There are too many areas they still rust out in with high acidic soil. Should be PVC only.
Posted By: Ryan_J Re: Rumors of 2008 changes - 09/13/06 12:13 AM
Regarding the expansion of AFCI's...I think the NFPA is setting itself up for a huge blackeye with this one. Considering the fact that the AFCI's must be the combination type, and nobody has a functioning AFCI type available yet, I can't see how the NEC would require a device to be installed throughout the entire house, when we don't even know if it works!
Posted By: rmiell Re: Rumors of 2008 changes - 10/14/06 02:42 AM
My son was just troubleshooting an AFCI bedroom circuit, in a remodel that he did not rewire. Every time a floorlamp was plugged in, the AFCI tripped. The homeowner even tried a different lamp, but still would trip.

My son, correctly, it turns out, tried looking at the room's light fixture first, and as soon as he took the canopy off, he saw the problem. The allthread rod was turned up so much inside of the fixture that it had scraped off the insulation.

I'm not sure which wire was in contact, but in this case, the AFCI did indeed work.

Rick Miell
Posted By: gfretwell Re: Rumors of 2008 changes - 10/15/06 03:47 PM
The neutral was grounded and as soon as there was some load on the circuit part of that load current leaked out the ground. The 30ma ground fault protection trips the AFCI
Posted By: Samurai Re: Rumors of 2008 changes - 07/27/07 03:04 PM
I think the AFCI requirement is squarely the blame of those of us with longer experience and with responsibilities as trainers and teachers of the newbies; by failing to emphasize the most basic and critical skill development - requiring the newbies to make absolutely sure that a (tight) really really firm connection is made at all junctions and terminations. (I went behind a crew with a three year "leadman" and helper[s] of unknown experience to hang lights and hot check-the rest of the devices had ben installed; everything checked fine at first - and then my helper started calling my attention to failing items I had already tested. on pulling the devices out wire-nuts would fly everywhere from lousy connections flying apart - we had to re-make-up the entire house -this was new work executed by employees who believed themselves to be electricians)
Posted By: sparkyinak Re: Rumors of 2008 changes - 07/29/07 05:17 PM
I agree with you Samurai to a point. In the constant envioronment of hurry up and get it done, sloppy work preveils. These new rules is just a band aid fix for that.

Although I am personally against the pending AFCI rules, it was only going to be a matter of time just because our society is that way.

I have replaced many burnt out receptacles and wirenuts and connections that an AFCI would have likely caught. The posting about the lamp tripping the AFCI was an easy fix. Imagine for a moment that you were called in to T/S an old wiring system that had an AFCI tripping and it was not due to a light fixture or something being plugged in. It would be like trying to find a needle in a pile of needles. With no as-builts and no way of nowing how it was wired and rewired of the last thirty years, it will not be an easy fix.

AFCI are to prevent fires with is a life and death matter and I am alright with that. I feel that it should be the home owner's decision with finacial support from the insurance and the home financing industry.

Although I preach until I am blue in the face to homeowners about how GFCI are there to protect, 99.9% of the complaints I get about them are they are defective that turns out that they are actually doing their job. It is the device they are plugging in that is a defective. If society in general can not grasp the basics about GFCI, how will they comprehend the complexity of AFCI.

As an electrician, think how are you going to explain to a customer that you billed them for several several hours of having them moving furniture, bookshevlves, and personal property so you can pull out receptacles to inspect; keeping in mind that if you disassemble the device, you must re-install it to meet today's code and you still can not be certain that you fixed the problem? Just because the breaker did not trip, does not neccesary mean that it was properly fixed.

Let's say it was tripping because of a loose connection causing some arcing within a wire nut. You spent hours pulling out devices and checking all the connections. Did you just re-tightening every thing or did you pull every connection apart to inspect the connections to ensure they are not burnt and covered in carbon? How many old connections that you came across that are crimped and taped or were a real pain in the kiester to get to because the original installer wanted to save 2" of wire? How will you warranty your work?

That formally loose connection is now cover in carbon may no longer carry the ampacity of the circuit. If this is the case, what will happen next? It will overheat and we all know where this can lead.

Granted my example is worst case scenero, however it is not all that unrealistic. Think of all the houses you have been in and if AFCI's were required just 10 years ago, how difficult would it been to T/S an AFCI tripping? Just look at your own home if you had to T/S one.

What will the homeowner do when he can not reset the breaker or do not want to pay out hundreds of dollars for an electrician? Extension cords and we all know how safe they are.

Bean counting may seem to be putting a price on someone's head. If you start running the numbers on the finacial impact of the changes in relation of the potential numbers of lives that would be saved, the money could be better spent on finding a cure for cancer. That will save more lives.

I understand the drive behind the proposed changes. Part of fire departments and safety orginziations mission is reduce fires and the loss of life. I feel that that it short term fix that will be a bigger finacial drain in the future. I feel that better technology and standards would reduce the numbers of fires without the finacial impact. For example, eliminate the use of stab-in connectors would be a big step.

Improved education in not only how to do a good splice/connections, but how to route wires so you will not have the need to put 50 wires under one wire nut and the boxes are not over filled.

When I plan a wiring project, I lay it out to keep the spices to a minimum. Each splice is a potential fire hazard down the road. after splicing or making a connection, I closely inspect my work to ensure it's a quality connection.
Posted By: Elviscat Re: Rumors of 2008 changes - 07/30/07 06:32 AM
sparkyinak, an AFCI will not trip due to arcing in a wirenut, it may not even respond to arcing between a hot and a neutral, a couple days ago I was sent to a house to install a couple devices (they wanted a couple recepticles changed to diferent styles, and we bought one to few smoke detectors) well I was working on a smoke detector, conected to an AFCI circuit in a bedroom, (the smoke was not actually in the bedroom) so I killed the breaker that the boss thought fed it, and then I stuck my induction pen in the box to double check, well turns out I didn't double check well enough (learned to triple check after the wires are pulled out) and I stripped the neutral, and while I was stripping the hot KRACK!-POW! big blue arc, partially melted strippers, blackened copper etc. I then held my induction pen up to the wires once more, and it read hot, so I went to the basement, killed all the AFCI's and went back up, yup, they were dead now, and I'm down a pair of strippers, not to mention I've lost some faith in AFCI's, even in a "parallel fault" the exact type they're supposed to detect!

We can legislate and legislate, but electrical work will always be able to cause fires and kill people, and it's personal responsability that needs to be emphasised, not every new, stupid, expensive gadget, in 20 years it'll cost tweice as musch to wire a house, and there'll be, maybe, a couple dosen less house fires a year. Ridiculous.

-Will
Posted By: resqcapt19 Re: Rumors of 2008 changes - 08/01/07 11:14 AM
sparkyinak,
Quote
I have replaced many burnt out receptacles and wirenuts and connections that an AFCI would have likely caught.

AFCIs, even the new "combination type", do not directly connect that type of fault. They will only detect that type of problem when the fault causes enough damage to make a ground fault or parallel arcing fault.
Don
Posted By: JJM Re: Rumors of 2008 changes - 08/03/07 05:08 PM
FYI: I've had brand new, out of the box TVSS receptacles cause AFCI breakers to trip. So if you have an AFCI breaker tripping on a brand new installation with nothing plugged in, suspect the TVSS receptacles (and I suppose GFCI receptacles might not be immune either).

Needless to say, until we discovered the problem, this was a REALLY vexing ordeal... bringing out the meggar, undoing all the connections, testing each cable run by run, only to find out in the end that two TVSS receptacles were causing the problem. No arcing in the receptacles, the green lights were on, and the grounds were good. Replaced the two new TVSS receptacles with other new ones and the problem went away.

And I'm supposed to put these things on smoke circuits if they cover bedrooms? Not in MY house.

Seems AFCI's are pretty effective at tripping when I use a saw or drill - trips right away - but when there is actual dangerous arcing as many of our shared experiences here seem to indicate, the AFCI just keeps the pretty blue sparkling going.

Joe
Posted By: Theelectrikid Re: Rumors of 2008 changes - 08/03/07 06:49 PM
Quote
I agree with you Samurai to a point. In the constant environment of hurry up and get it done, sloppy work prevails. These new rules is just a band aid fix for that.


I agree with both (all) of you, and I'm not even an electrician! (Or apprentice for that matter.)

These (50+ year old) Levittown (tract) houses are wired better than any new Toll Brothers box.

Ian A.